NEC Omissions - Electrical - DIY Chatroom Home Improvement Forum
Old 02-17-2009, 09:10 AM   #1
NEC omissions
If the NEC and the AHJ is silent on some issue, e.g., I don't know, like putting a small fan in a resi. panel to equalize CB temperatures by circulating the air in the panel, is anyone allowed to install this fan?
Old 02-17-2009, 09:12 AM   #2
Remodeling Contractor
no. NEC covers this by specifying that no device or material is to be used for a purpose not specified by its UL rating.
Old 02-17-2009, 10:51 AM   #3
So far, so good.
http://www.nhpa40.org/b2b/pics/Computer_Fan.jpg
If this fan is UL listed to move air within a certain ambient temp, then it's OK to use?
I can't imagine UL anticipating every possible usage of their listed products (unless they have some catchall phrase that prohibits "other usage").
Old 02-17-2009, 12:04 PM   #4
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Why would a fan like this be necessary? In a properly wired panel with good connections is there any substantial temperature rise? Maybe if it is very heavily loaded?
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 02-17-2009, 01:28 PM   #5
joed's Avatar
Rewards Points: 13,740
Jamie
It would not be needed. Cooling is not needed in a breaker panel.
It would void the testing and approvals of the panel not the fan. The panel is encolsed to contain any fire. The fan would let the fire out in the slim chance there was a fire. It would also fan it and make it more intense.
Old 02-17-2009, 02:08 PM   #6
A guy is having occasional breaker trips with an HVAC system. The fan, not vented to the panel outside, might let him squeak by by equalizing the hot breaker temp.
Another way would be to hand select breakers that trip on the high side of the tolerance band but that method is not too practical.
Design revision A; wire a NC overtemp switch in series with the fan.
Old 02-17-2009, 02:25 PM   #7
He needs to diagnose and address the problem not treat the symptoms.
If you car leaks coolant, you don't duct tape a bucket under it to catch the fluid then pour it back in every day.
220/221 is offline   Reply With Quote
Old 02-17-2009, 02:31 PM   #8
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Bad compressor valves, short cycling, installed the minimum vs. max OCPD?
wirenut1110 is offline   Reply With Quote
Old 02-17-2009, 05:52 PM   #9
It's so infrequent and seems to have to do with the Aux heat having to come on with his 3C nighttime setback, that maybe 1 out of 5 breakers picked at random might work for him, but there is no practical way to do this experiment.
We'll see what clamp-on meter says.
Old 02-17-2009, 08:45 PM   #10
Rewards Points: 150
I thought this was a hypothetical question. I have to start reading more carefully!
Gary
Gary_602z is offline   Reply With Quote
Old 02-17-2009, 11:10 PM   #11
Idiot Emeritus
Rewards Points: 1,492
One of the local casinos I work at occasionally had a 2000 amp 480 volt breaker trip one day. Their solution was to remove the cover, and place a fan to blow cool air at the breaker. A few days later, me and 3 other guys were replacing a 1500KVA transformer. It weighed about 6000 lbs. It wasn't fun.
I build industrial control panels occasionally, most of them have some sort of cooling system. It can be a simple fan, or an A/C unit specifically designed for the purpose. The biggest problem I have with any type of fan in a control cabinet is dust getting all over EVERYTHING. Even if it's in a clean area, and filters are changed regularly, it still gets in.
The fans, etc. in the control panels are because there is heat producing equipment inside, not to keep a breaker from tripping. Sometimes, you'll see fans connected to large industrial panels, motor control centers, and such, that are installed in dusty environments. The fans are always outside, and their purpose is to maintain a slightly positive air pressure in the panels. This way, dust cannot get in. (It does anyway though, just not as much.)
It shouldn't be too hard to figure out why the breaker trips, and solve the problem once and for all.
Rob
micromind is offline   Reply With Quote
Old 02-17-2009, 11:21 PM   #12
Registered User
Termite's Avatar
If the AHJ is silent on this scenario, they're dropping the ball. It should be prohibited unless both the panel and the fan are listed for use in conjunction with each other.
Just because the NEC doesn't expressly prohibit something doesn't mean that you can do it.
Old 02-18-2009, 10:04 AM   #13
I'm thinking no fan. . .thanks, folks. . .
Old 02-18-2009, 12:33 PM   #14
DIYer
Computer fans are never UL listed.
Components can have the RU recoginized component mark, but never get a UL mark.
Gigs is offline   Reply With Quote
Old 02-18-2009, 12:56 PM   #15
I think the problem is solved. There were other loads on that same 100A breaker. Rewire!