-   -   NB Cable inside conduit - ok for outdoor use? (http://www.diychatroom.com/f18/nb-cable-inside-conduit-ok-outdoor-use-108495/)
JSAustin 06-22-2011 06:19 PM
I am thinking no way - but figured I should ask the experts. I have some new #8 NB cable I want to run to a irrigation pump for 70 feet. This conduit will be under an existing wood deck (i.e.outdoors) but above grade. To complete the 140 foot run to the pump, I would add a junction box and convert the wire to #8 THWN and a #10 THWN ground wire as the remaining run of wire will be underground. Would this fly with the inspector?
brric 06-22-2011 06:21 PM
If you mean NM cable the answer is no. Not allowed in wet locations, even in pipe.
mpoulton 06-22-2011 06:30 PM
The inside of conduit in a wet location is considered a wet location. Rightfully so, because it always seems to get (and stay) even wetter and grosser than the surroundings!
JSAustin 06-22-2011 06:44 PM
Yes NM-B - Thanks that was my thoughts as well...
Yes I did mean NM-B - Thanks!
frenchelectrican 06-23-2011 01:51 AM
First thing first .,, No NM cable are used in outdoor location at all even with conduit { pipe }
Second thing is how big this pump is ? et what voltage you are plan to hook it up as well.
Merci,
Marc
frenchelectrican 06-23-2011 02:21 AM
the computer got screwy on moi opps.,,
JSAustin 06-23-2011 04:17 PM
The whole NM-B discussion is a lost cause as I expected.
To answer your 2nd point .. 115 volts - 1 hp - draws ~16 amps when running - #8-2 with #10 ground UF wire about 140 feet, circuit breaker set at 30 amps.
frenchelectrican 06-23-2011 09:51 PM
Do this pump motour have exteral overload or interal overload protection ? if not then you will have to down size the breaker down to either 20 or 25 amp breaker otherwise if the motor stall it may not trip the 30 amp breaker if have overload protection then you are fine with part due the NEC code can allow up to 250% of FLA rating of the motour.
Merci,
Marc
JSAustin 06-29-2011 06:10 PM
Yes the 1 HP motor has internal thermal protection so no external protection required. As of today, the project is ready for the inspector...
rbj 06-29-2011 09:29 PM
Gfci?
JSAustin, No NM-B to wet location. UF-B could be direct buried w/o conduit. In either case be prepared to install a GFCI breaker if local code is NEC.
JSAustin 06-30-2011 03:45 PM
Thanks RBJ for the heads up.
This is a dedicated circuit to the pump (Also approved for outdoor use). There will be no 115 ac outlets installed on this circuit so no contact to humans. Mr. Inspector will let me know if I need a GFI to meet The Code. Either way - I will post his findings after inspection.
frenchelectrican 07-01-2011 12:18 AM
I don't think so you don't need GFCI however there may a local code requirement that it will need it for irriagtion pump.
Merci,
Marc
rbj 07-02-2011 02:54 AM
Gfci?
Merci,
Marc
Hi Marc, In domestic and bodies of water (Ponds, irrigation) check out [682.23(B)] where like well pumps and pool pumps...are being hit for GFCI installs up to 60 amps.
frenchelectrican 07-02-2011 10:48 PM
Rbj.,
I will not challange you but the 682.23B is for pool system so the irriration for watering the feilds do not use the GFCI at all unless I stated only if the local code do show up but I know in State of Wisconsin the irragation water pump do not use the GFCI at all unless you are next to the pool pump and for subersable well pump never use the GFCI at all.
If the submersable pump used for fonation water only then Oui GFCI protected.
BTW French codes are pretty simauir to this so there is no Conneries on this matter.
Merci,
Marc