MWBC To Outbuilding? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-11-2013, 10:56 AM   #1
MWBC to outbuilding?
I know this is everyone's favorite topic... I am installing a storage building and would like to have a couple of 20A circuits for lighting and battery maintainers for lawn equipment. Originally, I was going run a single circuit, to avoid the expense of installing a subpanel and grounding rods at the shed, but I've heard that an MWBC can be used to supply an outbuilding without using a subpanel and grounding system. Is this true?
Here's an overview of the set up:
  • 10'x14' building at the back of the yard. Will be used for general storage and lawn equipment.
  • Wire run from subpanel in garage to the shed location is about 90'. Run will be in buried conduit.
  • I want to install lighting in the shed, as well as some convenience receptacles in and outside the shed, and an outdoor floodlight for the backyard.
I think a single 20A circuit would handle my needs, but a couple of circuits sounds appealing if the additional cost is not prohibitive.
I understand that the buried wire should be GFCI protected. My initial plan was to use a blank-face GFCI in the garage to accomplish this, but I don't think this would work on a MWBC.
Finally, is 12 AWG sufficient for a 90' run, or do I need to move up to 10 AWG, to account for voltage drop?
Is this doable, or am I headed down the wrong path here?
clashley is offline   Reply With Quote
Old 05-11-2013, 11:00 AM   #2
Electrical Contractor
kbsparky's Avatar
If the wire is buried in conduit, and at a proper depth, you do not need GFCI protection on the feeder.
However, you will need GFCI protection on any convenience outlets located in the shed.
Personally, I would not worry about voltage drop on such a short run.
Also, be advised that you will need a "disconnecting means" located in or at the shed. This can be accomplished by using something as simple as a double-pole wall switch, rated at 20 Amps or more.
-KB
Old 05-11-2013, 11:41 AM   #3
Rewards Points: 80
At 90', you are pushing the envelope for considering voltage drop. I think you are just fine, but you are getting close. I would run nothing less then #10 wire even on the 20 amp circuit. This gives you the ability to install a small 30 amp load center down the road should you need it. I would also pull 4 wires.
Its amazing how quickly we can take a 20 amp circuit and realize we need more power. When I am trenching, back filling and buying conduit, I always plan for expansion.
Old 05-11-2013, 12:32 PM   #4
Let me ask this... is the MWBC permitted? If I pull 4 10 AWG wires to support a 20A MWBC, wouldn't that essentially give me the same capacity as a small load center? I'm not opposed to the load center idea, but if I can get the same capacity with an MWBC, it seems like a more cost-effective solution.
The purpose of the shed is to get all the crap out of my garage, which will be workspace (and is already wired with a few circuits and contains a subpanel, so expanding service into the work area is relatively easy).
New plumbing for bathroom in outbuilding on slab mnschu Plumbing 6 04-02-2012 03:13 PM
MWBC to Garage Questions benleef Electrical 3 02-22-2012 12:02 PM
Line to line load on a MWBC? rjniles Electrical 13 12-09-2011 08:09 AM
Electric to outbuilding in backyard oscarmw Electrical 18 09-15-2011 07:36 AM
Questions about providing electricity to an outbuilding drichards Electrical 4 12-11-2010 12:07 PM