I'm installing an automatic transfer switch for a standby generator. I'm not an electrician, just a DIYer, but I have completely required a bathroom and such. As part of this transfer switch project, I've moved selected circuits from the main panel to the transfer switch panel (these are the circuits that will be powered by the generator). A few of these circuits appear to be "multiwire branch circuits", that is, there are black and red hot wires with a shared white (neutral) wire. I have 2 questions:
1) Every authoritative thing I've read says that the potential between the circuits that share a neutral must be 240v (that is, they are connected to different phases). This is the way they were wired in the main panel, and this is the way I've done it in the transfer switch panel. However, an electrician (who I actually had considerable faith in), insisted that it must be wired so that the potential across the circuits is 0v. I'm wondering if there is any possible scenario where this would be the correct answer.
2) In one case, one half of the multiwire branch circuits stays in the main panel, while the other goes in the transfer switch panel. Is this acceptable? If so, does it matter whether the neutral is connected to the neutral bar in the main panel or in the transfer switch panel?
Thanks.
Jeremy Hillary Boob, PhD is offline   Reply With Quote
Old 11-17-2008, 11:42 AM   #2
Each leg of the MWBC should be on opposite phases to avoid overloading the neutral.
jerryh3 is offline   Reply With Quote
Old 11-17-2008, 11:49 AM   #3
Rewards Points: 2,350
You are correct that the potential across the MWBC must be 240 V. If it is 0 V, then the neutral will carry the combined current in each leg, a recipe for danger. As to the second part, whether the neutral can be in one panel and one hot be in another, the answer is no. If you have to power one half of a MWBC from the transfer switch, then you must power both halves from the transfer switch.
Old 11-17-2008, 11:56 AM   #4
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Thanks.
If they are on the same leg of the panel, and you put a meter across the 2 hot leads, it will not read anything, as it has no path. It is like touching the same hot wire with a meter - no reading. THIS IS WRONG for a MWBC. I just recently wired my fist MWBC's but I am positive that they must be on seperate legs of the panel and the meter needs to read 240 if you test on both hot wires.
2008 code will require double pole breakers to ensure the power is from seperate legs of the panel.
Jamie
jamiedolan is offline   Reply With Quote
Old 11-17-2008, 02:04 PM   #5
240 across both hots, 120 between each hot and neutral.
rgsgww is offline   Reply With Quote
Old 11-17-2008, 03:00 PM   #6
Is the generator one with a 240 V/2 pole center tapped neutral output?
If so, there is no problem with MWBC wiring.
But, if the generator is 120V/1 pole, one of the poles of the MWBC should be dropped to avoid neutral over-loading!
Old 11-18-2008, 01:25 PM   #7
Thanks for all of the responses.
I'm not clear as to why both halves of the MWBC must be powered from the transfer switch. Can you explain the issue here? Thanks.
Old 11-18-2008, 02:24 PM   #8
DIY'er
jamiedolan's Avatar
They must have power from different legs of the panel (or generator) otherwise the shared neutral has no protection from overcurrent. You can MELT your neutral and start a fire, if you don't have the power fed from seperate phases.
If you have half fed from the generator and half from the panel and service is on from the power co, then your feeding that neutral with power from the generator and your feeding the neutral with power from the power co.
If you hook up both legs of a MWBC to the generator, then you must make sure that the generator is putting put power on 2 different phases. 120 each and 240 between hots.
Jamie
Old 11-18-2008, 02:40 PM   #9
joed's Avatar
Rewards Points: 13,346
Power comes back on and you have power from two different sources feeding through the neutral. They are not in phase and who knows what would happen.
Old 11-18-2008, 03:16 PM   #10
Yes, this makes sense. Thanks.
Need a wiring diagram Mooreski Electrical 47 02-01-2015 03:07 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM
lighting circuit design question amakarevic Electrical 15 10-31-2008 02:11 PM
Circuit BReaker Question - breaker didn't trip and no power thru the circuit Ronin_67 Electrical 2 08-08-2008 06:06 AM
Branch circuit ?s Bcoleman6 Electrical 7 01-27-2008 10:27 AM