Multiwire Branch Circuit Question - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 06-15-2014, 07:39 PM   #31
Rewards Points: 158
Originally Posted by Jim Port View Post
Skoby, a GFI cannot be split wired like your old setup.
Yeah, it make sense now. I'm just new this wiring. Thanks, I think I get it.
skobydog is offline   Reply With Quote
Old 06-15-2014, 08:15 PM   #32
Rewards Points: 158
Can I use one GFCI on each circuit then go from the GFCI line side and feed the other two reducing the required GFCI receptacles to 2?
This is on a kitchen counter top.
Old 06-15-2014, 08:46 PM   #33
Electrical Contractor
jbfan's Avatar
Rewards Points: 650
Yes you can.
Old 06-15-2014, 08:48 PM   #34
Licensed electrician
Rewards Points: 1,876
The load neutral will need to come from the load terminals, not like shown in the diagram.
Old 06-15-2014, 10:21 PM   #35
Rewards Points: 158
If I understand what your saying, would I need to have a line neutral to each GFCI?
If so, I guess I'd have to run seperate circuits from my 12/3 to (2) 12/2s? Or am I way off?
Old 06-15-2014, 10:59 PM   #36
Rewards Points: 1,832
Originally Posted by jbfan View Post
Yes you can.
Look at the picture. It wont work. Any time a GFCI feeds through it must not share a neutral with anything. The second pic the OP has will work.
Jump-start is offline   Reply With Quote
Old 06-16-2014, 07:20 AM   #37
Master Electrician
Rewards Points: 3,964
Totally wrong. You have line and load reversed.
brric is online now   Reply With Quote
Old 06-16-2014, 07:24 AM   #38
Rewards Points: 3,396
Maybe a typo.(line, load reversed)
If not switch the terms line and load on drawing then wire that way.
(line to get common neutral, load to get separate two wire neutral)
ritelec is offline   Reply With Quote
Old 06-16-2014, 11:21 AM   #39
Rewards Points: 158
I had gotten the line/load mixed up last night while i was rushing the drawing.
Here goes another pic. Hopefully this one is it
Old 06-16-2014, 11:28 AM   #40
The pigtails are not needed, but can be used. The receptacles downstream can be regular duplexes.
Old 06-16-2014, 12:44 PM   #41
Rewards Points: 158
I'm confused where pig tails are required in a multiwire branch circuit.
I suppose i could just pig tail everything?
Old 06-16-2014, 12:56 PM   #42
jbfan's Avatar
Rewards Points: 650
Pigtails are required for the neutral wires on a MWBC.
Old 06-16-2014, 06:12 PM   #43
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
The Following User Says Thank You to stickboy1375 For This Useful Post:
Jump-start (06-16-2014)
Old 06-16-2014, 07:01 PM   #44
Rewards Points: 332
I agree with the Pros here. MWBC is fine if done properly. In fact, the kitchen counter receptacles would be a perfect place for this.
Of course, the GFCI requirement complicates things a bit, but 12-2-2 cable could be used too.
I re-wired almost all of my MWBC lines when my panel was upgraded simply because it was done sloppily and made no logical sense.
Outdoor receptacles shared with bathroom, kitchen shared with living room, etc...
sgip2000 is offline   Reply With Quote
Old 06-16-2014, 08:28 PM   #45
Rewards Points: 158
Originally Posted by stickboy1375 View Post
Thanks again
SER Cable for Branch Circuit & Wire Size sdmuleman Electrical 2 04-02-2014 11:02 AM
NEC - what is the purpose of some of these codes ? chez bouton Electrical 32 12-17-2013 02:04 PM
Circuit Breaker Troubleshooting Question - need help! DanLeonard Electrical 4 10-01-2012 11:20 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM
Wire size for dryer jamiedolan Electrical 14 01-15-2009 05:43 AM