Multiple Grounds Under One Screw In Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 04-16-2011, 06:48 PM   #1
Multiple Grounds under one screw in panel
Hi,
I have been reading some discussions where people are saying that it is ok to put two grounds under one screw, depending on the panel instructions.
I am running into some problems that others are having where there is still room for more breakers (4 to be specific) but only have one or two spots left on the neutral/ground bars.
I have a Murray LC120DC panel and it says the following: "Equipment ground bar terminals are suitable for the following combinations: Small Terminals: One 14 to 6 AWG CU; one 12 to 6 AWG AL; Two 14 AWG CU; Two 12 AWG CU; Two 12 AWG AL Solid Wires."
I left off the requirements for the large terminals because they don't apply to my question.
So, do the statements in bold say that it is ok to have to two grounds (12 or 14 guage wire) under one terminal? Is it only ok to do on one of the bars or is it fine for both?
Also, does anyone know why some panels allow for two grounds under one terminal and others do not?
Thanks.
dw1256
dw1256 is offline   Reply With Quote
Old 04-16-2011, 07:31 PM   #2
Licensed electrician
Rewards Points: 1,746
Grounding conductors can be doubled in your panel. These will be bare or green insulation. Grounded conductors need to terminate in a hole unshared with anything.
The difference is in the listing requirements and the electric code.
Old 04-16-2011, 07:37 PM   #3
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
it means exactly what it states.
you can put 2 copper # 14 wires under one terminal
you can put 2 copper #12 wires under one terminal
you can put 2 #12 aluminum solid wires under one terminal
No other combinations of multiple wires is acceptable. In other words, you cannot mix #12 and #14 under 1 terminal.
This applies only to ground wires and not neutral wires.
Old 04-16-2011, 08:29 PM   #4
Rewards Points: 1,532
Alternatively you can take a few ground wires (not neutral wires) off the bus bar, wire nut them to a short length of bare wire (size equal to the larger(est) of the group), and re-attach the short length leaving a few holes free for other wires.
Neutral wires must be connected to the bar to which the fat neutral of the service cable is attached, or to another bar with a metal strip between it and the former bar. Ground wires may be connected to any bar that has metal to metal contact with the back of the panel.
Grounded conductor -- Formal name of what we often call the neutral. Actual grounding properly occurs only at once place, where the first disconnect switch (e.g. the main breaker) for the power supply is.
Grounding conductor -- What we refer to as a ground wire.
Old 04-16-2011, 08:31 PM   #5
nap
You talking to me?
nap's Avatar
you can. I wouldn't. It looks tacky, IMO. I would install another ground bar.
Wiring a sub panel to another sub panel Uncle Wayne Electrical 25 02-08-2011 09:50 AM
Subpanel next to Main panel wired the same in 1990 Uncle Wayne Electrical 3 01-20-2011 12:43 AM
Multiple wires from Panel into same Switch eliddon Electrical 2 10-17-2010 08:34 AM
Multiple cables, mixed up grounds OK? Ultrarunner2017 Electrical 5 02-02-2009 08:03 PM
breaker panel question chadvavra Electrical 11 08-10-2007 09:20 AM