Old 09-18-2011, 10:42 PM   #16
Originally Posted by Code05 View Post
And you will bond all boxes, right?
I am confused between bonding and grounding.
I will connect ground wire to each box anyway. Is that the same as bonding?
I also forgot to let you know that this will be EMT conduit. I thought I could be off with this if I use EMT conduit with proper connection at the sub panel and junction boxes
thone is offline   Reply With Quote
Old 09-19-2011, 08:51 AM   #17
Code05's Avatar
Rewards Points: 1,104
Forget it. For you, they are the same.
Sounds good.
Not quite sure what you are saying here. EMT is fine.
Code05 is offline   Reply With Quote
Old 09-19-2011, 09:48 AM   #18
Rewards Points: 1,418
All ground wires (equipment grounding conductors) are connected (bonded) together wherever they come together. A metal box must be bonded to ground as well, for example using a pigtail to the bundle of ground wires or by appropriate properly installed conduit.
Old 09-19-2011, 10:14 AM   #19
Code05's Avatar
I know 250.148 well.
Old 09-19-2011, 10:32 AM   #20
Code05's Avatar
Thone, here are a couple of pics for you.
The Following User Says Thank You to Code05 For This Useful Post:
thone (09-19-2011)
Old 09-19-2011, 01:20 PM   #21
Thanks - Code05.
I notice that, in the picture, they are using multiple ground wires within one conduit. Can I use only one ground (same #12 as other conductors?) for each conduit?. I believe I don't even need a ground wire since I will be using EMT (and I can also use it as EGC), but just to be safe.
Old 09-19-2011, 03:21 PM   #22
Code05's Avatar
Thanks - Code05.
Yes one #12 is sufficient.
No, you do not have to install a wire EGC if you do not want to. The EMT can be the EGC, but there are other rules you must follow.
I recommend the wire EGC for a DIY installation.
Old 09-19-2011, 05:38 PM   #23
Rewards Points: 150
When using EMT, you dont need the EGC
Sunny B. is offline   Reply With Quote
Old 09-19-2011, 07:37 PM   #24
Code05's Avatar
Rephrase.
Old 09-19-2011, 08:42 PM   #25
Rewards Points: 150
Rephrase.
250.4(A)(4) Bonding of Electrically Conductive Materials and Other Equipment. Electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
*This is a quote from 2005. My 2008 isn't handy at the moment*
The Following User Says Thank You to Sunny B. For This Useful Post:
Code05 (09-20-2011)
Old 09-19-2011, 09:56 PM   #26
Electrician
SD515's Avatar
Rewards Points: 504
Rephrase.
My turn...
A conduit system of EMT made proper and continuious, with tight couplers and fittings at junction boxes and the like, can be used as the EGC, and no additional EGC conductor needs to be run within the pipe. Device EGC terminals can be connected to the metal box that supports it with a proper jumper.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
Code05 (09-20-2011)
Old 09-19-2011, 10:05 PM   #27
Rewards Points: 150
Originally Posted by SD515
My turn...
Your break down is 20x better than mine, but the conduit dosent have to be EMT
Code05 (09-20-2011)
Old 09-19-2011, 10:10 PM   #28
Electrician
SD515's Avatar
Rewards Points: 504
No it doesn't have to be EMT. But it can't be something like galvanized or copper water pipe either. It has to be a recognized wiring method conduit, metal, and complete (physically and electrically) to qualify to be an EGC. I only mentioned EMT because that was what was mentioned before.
Kyle
Code05 (09-20-2011)
Old 09-19-2011, 10:41 PM   #29
I will use grounding conductor as you recommend. -- Thanks
@Others, I also understand that EMT can be used as EGC and no additional EGC is required (thanks to you all). But I'm worried that I might not do things right with EMT connectors, etc.
Old 09-20-2011, 01:58 AM   #30
" Euro " electrician
frenchelectrican's Avatar
As long you have the EMT connector and set screws tight you are fine with grounding purpose.
Just take a older or other flat screwdriver which it will get damaged over the time and use that with a hammer or a niner { linemans pliers } and give a good whack on it you will have to do that few time to make sure it is good and tight.
And also pay attetion when you cut the EMT make sure you deburr it with rememer
Here the photo of this tool I use all the time it will have dual purpose one to deburr and also drive the set screw in without slipping.
They are about 15 - 25 Euros but it worth it if you doing alot of EMT's that photo show above that will work for half , three quarter and full inch EMT conduits.
I have 4 of them and I used it all the time. { two are standard sized and other two is metric sized due I am in France and we have metric conduits here. }
Merci,
Marc
Old House Rewire finnimus Electrical 15 05-13-2011 11:39 PM
upping neutral and ground conductors for multiple circuits crankcase Electrical 2 03-18-2011 01:37 PM
short circuit. reset the breaker, but no power bp91708 Electrical 10 03-18-2011 11:07 AM
Multiple Circuits - Same Outlet box Revnjeff Electrical 2 09-04-2008 09:17 PM
Sub panel grounding sluggermike Electrical 27 11-11-2007 02:23 AM