Multiple Circuits (separate Neutral) In A Conduit With Receptacles - Electrical - DIY Chatroom Home Improvement Forum
Old 09-18-2011, 01:48 PM   #1
Multiple circuits (separate neutral) in a conduit with receptacles
I am running multiple circuits (3 circuit separate neutral) in a 1/2" conduit. They will go to several junction boxes as well as junction which has receptacle on it. Is this ok to have a junction box with several circuits passing through (without connection) with receptacle?
thone is offline   Reply With Quote
Old 09-18-2011, 01:51 PM   #2
Code05's Avatar
Rewards Points: 1,104
Yes. Bond the box.
Code05 is offline   Reply With Quote
Old 09-18-2011, 02:00 PM   #3
You can pass circuits through junction boxes, as long as you do not exceed the fill capacity of the box. Also, depending on the gauge of the THHN in your conduit (and the type of conduit itself), you may be pushing the fill capacity of 1/2 conduit with three circuits using independent neutrals.
clashley is offline   Reply With Quote
Old 09-18-2011, 02:13 PM   #4
Code05's Avatar
You can get 9 #12 THHN in a 1/2" EMT conduit.
Old 09-18-2011, 04:32 PM   #5
Electrical Contractor
jbfan's Avatar
Rewards Points: 656
Is this single phase or 3 phase?
Single phase can not share 3 circuits.
Old 09-18-2011, 05:18 PM   #6
Rewards Points: 1,548
But the neutrals are not shared.
Old 09-18-2011, 05:18 PM   #7
This is single phase. What do you mean by cannot share 3 circuits?
Old 09-18-2011, 06:04 PM   #8
Missouri Bound's Avatar
If your intention is to share one neutral with three circuits on your single phase service.....you absolutely CANNOT do it.
Old 09-18-2011, 06:52 PM   #9
Code05's Avatar
Not applicable to your install. You have 3 hots and 3 neutrals.
Old 09-18-2011, 06:53 PM   #10
Code05's Avatar
Read the OP #1 post. No shared neutrals.
Old 09-18-2011, 07:46 PM   #11
jbfan's Avatar
Rewards Points: 656
I misread the OP.
Nevermind!
Old 09-18-2011, 07:52 PM   #12
I read the OP and wasn't sure what thone was going to do. Still haven't heard enough from thone to really know. It's the "seperate neutral", not seperate neutrals that made me question it.
Old 09-18-2011, 08:44 PM   #13
Code05's Avatar
good point.
Old 09-18-2011, 08:56 PM   #14
My bad!
Yes, I am planing to run separate neutrals for each circuit.
Thanks to you all!
Old 09-18-2011, 09:01 PM   #15
Code05's Avatar
My bad!
Thanks to you all!
And you will bond all boxes, right?
Old House Rewire finnimus Electrical 15 05-13-2011 10:39 PM
upping neutral and ground conductors for multiple circuits crankcase Electrical 2 03-18-2011 12:37 PM
short circuit. reset the breaker, but no power bp91708 Electrical 10 03-18-2011 10:07 AM
Multiple Circuits - Same Outlet box Revnjeff Electrical 2 09-04-2008 08:17 PM
Sub panel grounding sluggermike Electrical 27 11-11-2007 01:23 AM