Multiple Circuits Needs - Electrical - DIY Chatroom Home Improvement Forum
Old 06-06-2009, 12:35 AM   #1
Multiple Circuits needs
I have a 50, 30 and 20 amp circuit that need to be brought over to a pre-existing shop approx. 100' out. I was gonna run separate lines of 4 AWG for the 50a. #8 for the 30a. and #10 for the 20a. Each circuit dedicated to specific load requirements, having it's own sub-panel. The 50a is for a lighting array, the 30a for a/c and the 20a for regular use shop lights and such.
Layman
The Layman is offline   Reply With Quote
Old 06-06-2009, 06:21 AM   #2
It would much simpler to run 4 wires and add a subpanel for those things, and build in a little extra for future expansion.
Old 06-06-2009, 06:33 AM   #3
300zx's Avatar
Post
I Agree
300zx is offline   Reply With Quote
Old 06-06-2009, 06:54 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
It is also code required.
You can only run one multi-wire circuit or one feeder at most to a detached structure.
Speedy Petey is online now   Reply With Quote
Old 06-06-2009, 10:24 AM   #5
Rewards Points: 236
Thats right. See this NEC article.
225.30 Number of Supplies. Where more than one building
or other structure is on the same property and under
single management, each additional building or other structure
that is served by a branch circuit or feeder on the load
side of the service disconnecting means shall be supplied
by only one feeder or branch circuit unless permitted in
225.30(A) through (E). For the purpose of this section, a
multiwire branch circuit shall be considered a single circuit.
There are some exceptions, but they do not apply to your project.
Old 06-06-2009, 12:33 PM   #6
Thanks for the responses guys. OK, so how do I pull those 100 amps off those three main breakers ?
Layman
A lil help guys?
Old 06-07-2009, 12:20 PM   #7
Rewards Points: 502
You dont. You take those three breakers out and put in a 100 amp breaker and run the appropriate AWG size to the structure and put in sub-panel.
You cannot utilize all three breakers to get 100 AMP service.
Now, if you are really needing a 50, 30 and 20, you may want to consider running 125 or 200 amp service to this structure.
-Andrew
DIY hobbiest
AndrewF is offline   Reply With Quote
Old 06-07-2009, 01:13 PM   #8
The 50a is for a lighting array? Are you doing a night baseball field?
hayewe farm is offline   Reply With Quote
Old 06-07-2009, 03:45 PM   #9
Andrew, so if I'm interpreting this correctly; I need to replace the 3 breakers with 1 100amp ? Now, the breakers are in different parts of the panel so I need to move the pre-existing breakers (that are in use) to make room in an area to fit the 100 amp ? Then run my 100amp sub-panel ...............
hayewe yes that too lol
What gauge wire would you recommend for 100' feet out on 100amps ?
Thnks guys
Old 06-07-2009, 04:30 PM   #10
Let's start from scratch.
Forget adding up the circuits. It doesn't work that way.
What are the loads that will be in the panel. And by this I mean the actual draw?
I agree that you probably need a 100A sub-panel, but I am also pretty concerned that you are in over your head with this project.
Old 06-07-2009, 04:39 PM   #11
SP thank you for your help and concern I have a 50amp sub panel that will go off the 100 sub I plan on adding a 30a a/c unit to cool our shop space and need a 20a circuit to supply the shop with shop lights and other low amp needs
Not to sure about actual draw I'm over building for future needs
Old 06-07-2009, 07:42 PM   #12
I'd install a 125 amp breaker in the main panel, run 3 copper #2's and a #8, underground in 1 1/2 PVC, to a sub panel in the workshop. Don't forget the ground rod(s).
220/221 is offline   Reply With Quote
Old 06-07-2009, 08:42 PM   #13
Rewards Points: 502
This is my recommendation and similar to what I am doing as well. (except for running 100 amp service on #2s instead of 125 amp service and running 4 #2 copper.)
-Andrew
DIY hobbiest
Old 06-07-2009, 08:44 PM   #14
WHY #2? And WHY four???
Old 06-07-2009, 09:18 PM   #15
clarifying Layman's Electrical needs!
Just enhancing Speedy Petey's advice! Forget about the 50 Amp. Subpanel and other loads. You will be pulling everything off the 100Amp. Subpanel in the detached structure! And in the Main Panel, there should be space for the 125Amp. 2-pole breaker that will protect the sub-feed to the panel in your shop!???!!! Don't Drink and Drive!!!
spark plug is offline   Reply With Quote
replacing old wire on existing circuits... red86yota Electrical 9 12-08-2008 06:00 PM
Multiple Circuits - Same Outlet box Revnjeff Electrical 2 09-04-2008 08:17 PM
Multiple Sub Panel Installation Handyman2007 Electrical 26 12-31-2007 05:47 PM
Power circuits under leaky bathtub? Beren Electrical 1 07-23-2007 09:02 AM
One neutral for two circuits?? TronCarter Electrical 13 01-14-2007 08:21 AM