Multi Wire Branch Circuit Question - Electrical - DIY Chatroom Home Improvement Forum
Old 09-02-2013, 04:46 PM   #1
Multi wire branch circuit question
I have a multi wire red black neutral,
the Black is on one breaker and the red is on another breaker
the white neutral goes to the white neutral buspar,
my question is
I see that there is no ground
but if I pull a receptacle that is powered by this multi branch circuit
it does have a ground,
at this point does this sound correct?
the reason I am asking is
I have a tester that you plug in and I get a 2 yellows,
this is good this is correct but it is a weak yellow,
like it wants to say open ground but it can't,
I only have this issue on the
the multi branch circuit all the other receptacles are fine,
should I be tracing a ground wire somewhere?
I am more curious than anything else,
the multi branch powers several receptacles in the kitchen
as well as a outside receptacle,
another older outside receptacle was decommissioned by a electrician a few years back,
and I suspect that there might be a loose ground from where he disconnected it
my multi meter tester shows voltage from
hot to neutral 120
hot to ground 94 not good.
neutral to ground 12 ? Also not cool.
I have been mystified by this ghost in the machine for a few years.
The outlets are never used,
the outside receptacle connected to the circuit works as it should with no problems, no ground issues, and is very close to the inside receptacles.
I was thinking I could ground the receptacles to the known good ground & retest it..
Thanks,
mikedabike64 is offline   Reply With Quote
Old 09-02-2013, 05:01 PM   #2
MarginallyQualified
Rewards Points: 2,464
Originally Posted by mikedabike64 View Post
I have a multi wire red black neutral the Black is on one breaker and the red is on another breaker the white neutral goes to the white neutral buspar,
my question is... I see that there is no ground
Until the 60's it was uncommon for ANY circuit to be grounded.
Even today, most things that you'll plug in don't have grounds and so the receptacle doesn't really need to be grounded.
That you're observing this on a multi-wire circuit makes no difference.
The Following User Says Thank You to TarheelTerp For This Useful Post:
mikedabike64 (09-02-2013)
Old 09-02-2013, 05:13 PM   #3
ok
Thanks, so I am NOT crazy,
Old 09-02-2013, 06:26 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,938
If the receptacle is three-prong, then it must actually be grounded - or protected by a GFCI and marked "no equipment ground". It appears that you have an ungrounded circuit which was extended with grounded cable and grounded receptacles, but the grounding conductor was not run back to the panel. That is not code compliant or safe.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
Old 09-02-2013, 06:49 PM   #5
ok thanks,
Ok, that makes sense
Old 09-02-2013, 07:24 PM   #6
Rewards Points: 150
I actually came across the same thing today. Outlet with ground connected but back at j box, ground is snipped back to sheathing. I don't know why they didn't connect to the ground that was right in front of them. But I have a plug tester and the middle yellow lights up fine but the right one barely lights up. I reconnected ground at j box and tests fine
romex1220 is offline   Reply With Quote
Old 09-03-2013, 03:19 PM   #7
ground
romex you found the loose ground at the j box? glad you found it, I was afraid when i posted this that people would think I had a weird question, If nothing else least Iam barking up the right tree, the wiring to the receptacle is accessible via a crawlspace, maybe I will get lucky and find it closer to entrance.
Old 09-03-2013, 03:44 PM   #8
Rewards Points: 150
No, I found it at a j box. Ground was just snipped and not connected. Not sure if they ran out of wirenuts or crimp connectors
The Following User Says Thank You to romex1220 For This Useful Post:
mikedabike64 (09-03-2013)