I planned on stripping the outer sheathing where it comes into the box. Surely I'd be able to bend and loop those aluminum wires and get them into position without harming them. At least it seems like I should be able to do that.
Whether it seems like it or not, it is not legal.
What I would do is come out of the bottom of the meter socket to just below floor level and come in with a LB. Then install a 90 elbow or if that brings the conduit too far from the wall, install a 2nd LB down into the top of the panel.
You only need a #4 AL for the ground between the meter and the panel. Your ground rods and water ground need to come into the meter/disco outside. The neutrals and grounds need to be separated in the panel.
Old 07-01-2012, 11:26 AM   #17
Rewards Points: 272
What if I were to use copper entry cable? Would that be legal? If so what should I be looking for in terms of wire type and size?
speedster1 is offline   Reply With Quote
Old 07-01-2012, 11:39 AM   #18
k_buz's Avatar
Copper would still be too large to legally make the bend.
3/0 CU diameter = .584 in
.584x8=4.672 in
You could return the GE panel (one I don't like to begin with, but not going to start THAT argument) and buy a deeper panel and use copper. Then you would be legal to come into the back of the panel.
Here's one that would work.
http://www.homedepot.com/Electrical-...&storeId=10051
another
Old 07-01-2012, 11:46 AM   #19
jrclen's Avatar
Rewards Points: 514
I prefer to exit the meter socket out the back and enter the panel through the top. That keeps the conduit inside the structure and makes wiring the panel easier and neater. And code compliant. That is not always possible, but when it is, that is what I do. I like to mount the panel to a piece of 3/4 inch treated plywood which is fastened to the concrete or blocks. The plywood extends above the panel so I can staple the branch circuit conductors above the panel.
I use aluminum triplex rather than a sheathed cable assembly.
John
jrclen is offline   Reply With Quote
Old 07-01-2012, 11:50 AM   #20
k_buz's Avatar
You can't use triplex in this application. The main is outside.
Old 07-01-2012, 11:52 AM   #21
jrclen's Avatar
Rewards Points: 514
Okay, I missed that. I would still use non sheathed conductors.
John
Old 07-01-2012, 12:27 PM   #22
Rewards Points: 272
Not sure if this matters but there will be a 200 amp main disconnect in the outside meter socket along with a 200amp main in the load center.
Old 07-01-2012, 12:32 PM   #23
k_buz's Avatar
Because the main is outside, your panel is a sub panel and all the rules of a sub panel apply.
Old 07-01-2012, 01:53 PM   #24
Rewards Points: 272
I called a friend of mine and we were talking about this. He said I could use 2/0 copper through the back of the panel and he thought it was permitted for 200 amp service.
Old 07-02-2012, 02:55 PM   #25
Rewards Points: 272
I'm hearing multiple thins about 2/0 copper. One electric supplier in my town says I need 3/0 for 200 amp service. Says 2/0 is rated for 175 amps. Other supplier says its permissable in my town and that the electrical inspector is okay with it.
Internet searches show that some places allow it and others don't.
Old 07-02-2012, 02:57 PM   #26
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,882
If it is a residential service 2/0cu is allowed, and typical.
Speedy Petey is online now   Reply With Quote
The Following User Says Thank You to Speedy Petey For This Useful Post:
speedster1 (07-02-2012)
Old 07-02-2012, 05:57 PM   #27
Rewards Points: 272
Thanks. That's what I wanted to hear. I have the boxes mounted and ready to run the wire. Now I just need to figure out how much cable to buy.
Old 07-02-2012, 07:32 PM   #28
Rewards Points: 272
I keep reading and reading and reading and seem to run across lots of conflicting info. I'm going to use 2/0 copper and I assume a 1/0 ground. Since my meter is outside and my load center is inside and connected in a closed system with 2" PVC conduit is it a requirement that I use 2/0-2/0-2/0-1/0 SER cable with the sheath intact? Or is it permissible to use 3 individually marked 2/0 copper wires and a 1/0 ground wire assuming they are marked and rated for this purpose.
Old 07-02-2012, 07:38 PM   #29
Electrical Contractor
jbfan's Avatar
Rewards Points: 256
Either way!
The Following User Says Thank You to jbfan For This Useful Post:
Old 07-02-2012, 07:45 PM   #30
k_buz's Avatar
You can't use 2/0 ser. It would need to be 4/0 ser.
Basement Concrete Wall Framing Against Stairs Epicsoccer Remodeling 7 01-13-2013 04:11 PM
Wood panel to concrete block wall sgold33 Building & Construction 22 07-30-2011 12:14 PM
Thick leveling mortar bed OK for concrete block stem wall? dwoloz Building & Construction 6 02-20-2011 09:44 PM
Door opening in load bearing block wall SS396 Building & Construction 12 09-13-2010 06:27 PM
creating door in possible load bearing wall acerunner Building & Construction 6 07-05-2010 05:33 PM