Old 06-01-2011, 09:41 PM   #1
more on sub panel
ok i want to see if this is right, main panel has only ground bar with main ground and all neutrals attached to it. i am putting a 60 amp 2 pole breaker in and running the 2 legs to the main bus lugs in the sub panel. i would connect a wire from the main panel ground bar to where in the sub panel? (it has only one (neutral?) bar. )
waynebo is offline   Reply With Quote
Old 06-01-2011, 09:45 PM   #2
more on sub panel
Is this subpanel in the same structure as the main or detached structure?
Old 06-01-2011, 09:46 PM   #3
more on sub panel
same structure
Old 06-01-2011, 09:55 PM   #4
more on sub panel
You need four wires - two hots, ground, and neutral - ground and neutral separated in the subpanel, so you need a ground bar kit for the subpanel.
Same structure so no disconnect or ground rods (or ufer) needed at subpanel.
Old 06-01-2011, 10:00 PM   #5
more on sub panel
so my ground and neutral wires both connect to the ground bar in the main panel then split to separate bars in sub panel?
Old 06-01-2011, 10:01 PM   #6
Licensed electrician
more on sub panel
Yes....
Old 06-01-2011, 10:02 PM   #7
more on sub panel
correct -
Old 06-01-2011, 10:07 PM   #8
I ask the impossible!
more on sub panel
Like I said in the other thread, you will need to add a ground bar to the subpanel.
Please do NOT consider any "before" picture of my house as any kind of endorsement of any particular construction method. In fact, you should probably assume that if I post a "before" picture, I am posting it because I am soliciting advice on a proper replacement for one of MANY things done wrong by a previous owner.
WillK is offline   Reply With Quote
Old 06-01-2011, 10:21 PM   #9
more on sub panel
forgive my ignorance. neutral bar in sub is isolated from panel, ground bar connects to panel metal enclosure. and should i ground sub panel? how come sub panel came with out ground bar?i'll have to buy one? (but came with bonding screw)
Old 06-01-2011, 10:51 PM   #10
Missouri Bound's Avatar
more on sub panel
Yes, you will have to buy one. A small panel like yours is used as the main in some situations. It is because of that it doesn't come with a grounding buss. Wherever you bought the panel they should have the buss. And you will isolate the neutral and bond the ground.
Old 06-01-2011, 10:53 PM   #11
more on sub panel
Not adding them where they might not be needed is just another cost saving for the manufacturer.
Old 06-01-2011, 10:55 PM   #12
more on sub panel
And a way to get 500% markup on the part when you DO need it.
Old 06-01-2011, 11:07 PM   #13
more on sub panel
thanks all
Old 06-02-2011, 12:23 AM   #14
more on sub panel
The green screw that was included with the panel for connecting the neutral bus to the panel box, do NOT use it. That is only for when you are using that panel as a main panel.
I would grab pics of mine and add markings to illustrate, but I'm falling asleep in my chair. Maybe tommorrow.
Old 06-02-2011, 10:06 AM   #15
more on sub panel
thanks
Panel cleanup gdoucette Electrical 5 06-26-2010 03:01 PM
Sub Panel SoxFan Electrical 2 12-02-2008 11:16 AM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 03:15 PM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 04:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM