More Clarification On Detached Garage Sub-Panel - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 02-06-2009, 10:29 PM   #16
Electrician
Originally Posted by 220/221 View Post
Still confused. Anybody??
B = No 20 amp two circuit installations allowed?
D = No 50 amp circuits allowed?
Your looking at disconnect requirements. Not feeder requirements.
Re-read 225.39
chris75 is offline   Reply With Quote
Old 02-06-2009, 10:43 PM   #17
Ok, so that refers you back to 220 III - which basically indicates sum of the loads as the deciding factor
Old 02-06-2009, 10:57 PM   #18
Rewards Points: 506
Send a message via AIM to theatretch85
The feeder disco would be at the main panel so.....?
Crap. If so, I've violated that more than a few times. For me, a typical sub would be #8's and a 50.
No. The OCPD (Over Current Protection Device) or your circuit breaker is at the main panel. This is sized to protect the wires. The Disconnect is installed at the detached structure and is basically just a simple switch to simply disconnect the service with one "switch". Most often a fused disconnect is used (circuit breaker). No matter whether you use a non-fused disconnect or a main breaker at the detached structure, point D is saying that the disconnect must be rated for NO LESS THAN 60 amps.
Your feeder could be 40 or 50 amps with #8 or #6 wire, but your disconnect at the detached structure by code must be rated for no less than 60 amps. Anything greater than the OCPD at the source is just simply a disconnect and nothing more, since an overload would trip the OCPD in the main panel.
theatretch85 is offline   Reply With Quote
Old 02-08-2009, 12:06 PM   #19
WaldenL's Avatar
Rewards Points: 268
Lightbulb
Originally Posted by Stubbie View Post
Ground rods provide no path for the egc they provide a path for high voltage.. high current.. events like lighting that are at levels way higher than residential voltages. It takes those kinds of events to get earth to be forced, if you will into, a conductor of appreciable amounts of current.
Damn! You know how there's that moment when you get it (um, the lightbulb comes on, since this is an electrical discussion) and then you look back and say "How did I have a problem with that before, it's so simple"... Well, that line (and the rest of your post) was that lightbulb! Damn that seems so obvious now.
Appreciate the help!
WaldenL is offline   Reply With Quote
Detached Garage Sub Panel Grounding Q integlikewhoa Electrical 15 03-12-2015 07:02 PM
Light Switch to Detached Garage - Grounding Issue smitty286 Electrical 1 10-22-2008 12:17 PM
Next Question, Sub panel in detached garage... OmegaBunny Electrical 5 09-15-2008 11:37 PM
detached garage Kapt Electrical 12 01-17-2007 08:37 AM
Detached Garage Sub Panel MainePainter Electrical 6 08-25-2006 09:58 AM