Is this MLO panel install code compliant?
Thank you,
Mike
Mike2401 is offline   Reply With Quote
Old 10-13-2010, 07:13 PM   #2
Licensed electrician
Rewards Points: 1,028
More details are needed. Prior to the 08 NEC this might have been ok to an outbuilding that had no metallic path back to the main building. The outbuilding panel was allowed to be re-bonded.
Under the 08 a four wire feeder is now required and the neutrals and grounds are isolated.
Where is the service panel?
Old 10-13-2010, 07:19 PM   #3
Hi Jim,
This is on an undeveloped property. The panel is the service panel. It is mounted on a pole right under the meter. It was installed sometime in 2005 and is being used for power and lighting for camping trailers during the hunting season.
Mike
Old 10-13-2010, 07:43 PM   #4
joed's Avatar
Rewards Points: 11,590
The cord hanging out the window is not code compliant.
The Following User Says Thank You to joed For This Useful Post:
Mike2401 (10-13-2010)
Old 10-13-2010, 08:24 PM   #5
I don't see a bond screw installed nor am I sure if this panel is rated for service equipment use.
Since it is deer season and your are in MD I can bring my bow and check it out.
Old 10-13-2010, 09:24 PM   #6
Thank you for your responses. The property is located in West Virginia . I believe Hampstead County. It was inspected and installed in 2003 not 2005 as previously thought. Inspection sticker says 2003.
Regards,
Mike
Old 10-13-2010, 09:55 PM   #7
" Euro " electrician
frenchelectrican's Avatar
Regards,
Mike
Ok with your county codes it was legit that time but you are missing a bonding screw but here one major gotcha once you get over 6 circuits you will have to change that to main breaker box set up I know it kinda pain in butt but the code is very specfically say no more than 6 throws { it don't matter if single or double pole verison } once get over that number you denfiely need main breaker.
Merci.
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
Mike2401 (10-14-2010)
Old 10-13-2010, 09:59 PM   #8
Electrical Contractor
kbsparky's Avatar
This panel is a Square D QO612L100RB, and it is rated for use as service equipment.
The bond screw belongs here:
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Old 10-13-2010, 10:05 PM   #9
Thanks KB, thats where I thought the bond screw would go. Like I said I was not sure about the service equipment rating. The only time I install something that small was for a subpanel.
Old 10-13-2010, 10:10 PM   #10
kbsparky's Avatar
We use those all the time on temporary pedestals. No main breaker required.
-KB
Old 10-13-2010, 10:16 PM   #11
as long someone don't have a funny idea with twinner in this one.
Merci.
Marc
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 03:57 PM
Sub Panel SoxFan Electrical 2 12-02-2008 11:16 AM
Is this kitchen remodel code compliant? jheavner Electrical 18 10-07-2008 11:01 AM
Moving several circuits to sub panel WoodworkerDave Electrical 2 09-27-2008 03:05 PM
Hardie Panel install? vern96 Building & Construction 1 07-01-2008 07:03 AM