Mixing Old Wire And New Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 09-04-2013, 05:40 PM   #1
Mixing old wire and new wire
While remodeling a house, I opted to keep some of the old wiring even though the walls are open and I could have replaced it. Is there any problem with mixing old wires with new wires? The old wires date back to the 60s. It is black romex cable with a ground wire. The sheathing is in good condition..not brittle, or damaged in any way. The only thing I question is that the ground wire is a smaller gauge than the white or black.
rojo527 is offline   Reply With Quote
Old 09-04-2013, 06:08 PM   #2
JuzRick's Avatar
Rojo: I see nothing wrong with doing that, it doesn't violate any NEC Regulations as to my knowledge; especially if the insulation still is in tact, doesn't show any sign of wore, everything ohms out as it should and your going back with the same conductor awg adjoining the existing conductor.
JuzRick is offline   Reply With Quote
The Following User Says Thank You to JuzRick For This Useful Post:
plummen (09-04-2013)
Old 09-04-2013, 06:39 PM   #3
MarginallyQualified
Rewards Points: 2,464
say la vee
Old 09-04-2013, 07:11 PM   #4
Licensed electrician
Rewards Points: 1,892
I would have replaced ALL the old wiring since the walls were open.
Speedy Petey (09-05-2013)
Old 09-04-2013, 07:33 PM   #5
Electrical Contractor
jbfan's Avatar
Rewards Points: 650
Even more so with the smaller ground wire.
jbfan is online now   Reply With Quote
Old 09-04-2013, 07:36 PM   #6
Rewards Points: 150
I agree with Jim. I don't trust older wiring whether it looks to be in good condition or not. Replace it now while the walls are open because if you do have a problem with it, you will have to open up the whole wall you just put up and painted. And with the small ground wire, there is more resistance in it than todays 12 and 14 gauge ground wires. Electricity always takes the path of least resistance which may be you.
romex1220 is offline   Reply With Quote
Old 09-04-2013, 07:50 PM   #7
Electricity takes all paths, not just the least resistance path.
The Following 3 Users Say Thank You to Jim Port For This Useful Post:
brric (09-04-2013), Speedy Petey (09-05-2013), stickboy1375 (09-05-2013)
Old 09-05-2013, 04:08 PM   #8
JuzRick's Avatar
I agree with you Jim. On the other hand, if he has already closed the wall, begun with the prep work; it's really nothing can be done. I would have gut the wiring; again reiterating: if the old wiring shows no signs of fault, then there shouldn't be any problems down the line. The ground should be in suitable shap too.
Old 09-05-2013, 05:23 PM   #9
My original intention was to just add a couple of receptacles in each room, and rewire the kitchen and bathrooms to code. Little by little, the project has grown to rewiring most of the house. I've been resisting changing the old wiring but I see your point. Unfortunately, changing the old wiring led to rerouting cables and adding new circuits. I added so many new circuits, I need to add another panel for breakers. As you can guess, the real problem is budget and time.
Old 09-05-2013, 06:10 PM   #10
JuzRick's Avatar
Normally a 30/30 circuit panel will accommodate the necessary loads you need, depending on the house sq ft and devices your installing. Recess Lights,the type, it's rating, how many your installing takes allot of space, qualifies for dedicated circuits per room that where you won't overload the circuit. Not saying that's what you are doing, just speaking in general where it will require you to have a 40/40 circuit panel to accommodate for all required loads.
What size panel you currently have?
Old 09-06-2013, 04:38 PM   #11
I have a Square-D panel with 42 breaker slots. I started buying the dual tandem breakers but it looks like I have to change most of the breakers to AFCI and they don't come in the tandem configuration.
Old 09-06-2013, 05:12 PM   #12
JuzRick's Avatar
Ok I see; yeah that very is a problem there. Depending on how many additional circuits you looking at adjoining to what you have existed, you could go with a 100amp 12 circuit panel for subfeeding purposes. You just have to calculate the difference between your existing service where you won't over exceeding the current ampere.