Mixing 14/2 and 12/2 wire on one circuit?
I am doing a bathroom remodel and have a 20 AMP circuit with only a single outlet and 12/2 wire. I have two other outlets that are already wired with 14/2 wire. I would like to put the outlets on the same circuit and wondering if it is okay to mix the 14/2 and 12/2 wires on the same circuit IF I swap out the breaker to a 15 AMP. I've calculated the load and the 15 AMP would be sufficient.
I know I could not mix in the 14/2 on teh 20 AMP circuit but I believe it is okay to mix them on the 15AMP.
dekohl is offline   Reply With Quote
Old 03-12-2012, 05:06 PM   #2
Happy to help
Lighting Retro's Avatar
you can run wire above code minimums without issue, but your capacity on the circuit is related to the smallest conductor on the circuit. Sounds like you have determined this is not an issue for you, and you might save a few bucks by using material you have in stock vs buy a new roll of wire when you only needed a few feet.
Lighting Retro is offline   Reply With Quote
Old 03-12-2012, 05:17 PM   #3
Love for Construction
<*(((><'s Avatar
Where are you located? Codes will vary by location.
Here in the states one is required to have one of the following scenarios for bathrooms:
1)OUTLETS in multiple bathrooms can be on a shared 20 amp circuit.
OR
2) You can have a dedicated 20 amp circuit for ONE bathroom's outlets, lights, fan, etc on one.
But in the case you suggest you would not be meeting current code standards only having 15amp capacity.
-luke-
<*(((>< is offline   Reply With Quote
The Following User Says Thank You to <*(((>< For This Useful Post:
jbfan (03-12-2012)
Old 03-12-2012, 08:12 PM   #4
Pure Genius
NEC states that whatever gauge you start a circuit with you must end the circuit with that gauge.
Dierte is offline   Reply With Quote
Old 03-12-2012, 08:22 PM   #5
Electrical Contractor
Do you have a code section to back that up?
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 03-12-2012, 08:35 PM   #6
Pure Genius
Let me look.
Old 03-12-2012, 10:28 PM   #7
Missouri Bound's Avatar
...and you should leave witrh the girl you brought to the dance.
Do you want it your way or the right way?
The Following 2 Users Say Thank You to Missouri Bound For This Useful Post:
Dierte (03-13-2012), plummen (03-13-2012)
Old 03-12-2012, 11:42 PM   #8
Licensed electrician
You will not find it in the code book Dierte.
i would not remove 1/4 of the circuit capacity just to keep the 14-2 in the circuit. Remove it and keep the 20 amp capacity.
Old 03-13-2012, 05:42 AM   #9
Pure Genius
I stand corrected. Must have been one of those things I was told long ago.
Old 03-13-2012, 06:01 AM   #10
seansy59's Avatar
14/2 on 15 amps
12/2 on 20 amps
You can never have 14/2 on a 20 amp circuit.
seansy59 is offline   Reply With Quote
Old 03-13-2012, 07:30 AM   #11
Originally Posted by seansy59 View Post
14/2 on 15 amps
12/2 on 20 amps
Never is a long time.
There are times when it is allowed.
The Following User Says Thank You to jbfan For This Useful Post:
Julius793 (03-15-2012)
Old 03-13-2012, 07:30 AM   #12
Master Electrician
14/2 on 15 amps
12/2 on 20 amps
Oh really. Got a code section to back that up?
busman is offline   Reply With Quote
Old 03-13-2012, 08:19 AM   #13
14/2 on 15 amps
12/2 on 20 amps
Might want to check out motor circuit or HVAC sizing.
You would be correct for general purpose circuits.
Wire Choice 12/2 or 14/2 Pentium Electrical 13 05-05-2011 04:33 PM
14/2 or 12/2 Wire? DIYHACK Electrical 14 01-15-2011 11:19 PM
Two Different Wire gages on Same Circuit OK? Lovegasoline Electrical 5 12-02-2009 06:00 PM
12/2 wire vs "heater wire" shtoink Electrical 11 11-23-2008 03:16 PM
Using 14/2 wire on 20 amp circuit mohairy Electrical 1 12-29-2007 07:26 AM