Missing Bonding Screw In Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 04-09-2013, 08:49 PM   #1
Missing bonding screw in panel
I have a slightly older Siemens panel, G2020B1100CU, and it is missing the green bonding screw that goes through the neutral lug into the panel. I plan to have this inspected. I know that I could just use a jumping strap to tie the neutrals to the panel, but not sure if the inspector will go for that.
In case you can't see from the photo, the two neutrals are strapped together and there is a separate ground bar that is connected to two ground rods.
I would like to just install a jumping strap from the ground bar to the neutral bar, or neutral bar to panel.
If I can't do that, does anyone know where I can get the bonding screw? I called Siemens tech support and they didn't have a part number and several local suppliers couldn't help either.
Thanks!
Justin
Note: I wrapped the neutral with white in between photos.
Missing bonding screw in panel-2013-04-09-16.01.36.jpg   Missing bonding screw in panel-2013-04-09-12.12.43.jpg
justinae is offline   Reply With Quote
Old 04-09-2013, 09:10 PM   #2
Master Electrician
Rewards Points: 3,678
Main panel or sub? 4 wire feed makes it appear to be a sub.
brric is online now   Reply With Quote
Old 04-09-2013, 09:30 PM   #3
Absolutely no reason to bond the neutral in this panel.
ren79eg is offline   Reply With Quote
Old 04-09-2013, 09:33 PM   #4
Master Electrician
And you know that how?
The Following 5 Users Say Thank You to brric For This Useful Post:
electures (04-10-2013), mpoulton (04-09-2013), sirsparksalot (04-10-2013), Speedy Petey (04-09-2013), stickboy1375 (04-10-2013)
Old 04-09-2013, 09:37 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
It would SEEM that way, but there is NO way to tell without more info from the OP.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 04-09-2013, 09:41 PM   #6
Cletis said so.
Old 04-09-2013, 09:43 PM   #7
sorry. subpanel in detached garage
Old 04-09-2013, 09:45 PM   #8
Electrical Contractor
kbsparky's Avatar
From the pic, it appears that there are 4 wires emerging from the conduit with the feeder wires in it.
The 4th conductor appears to go across to the left, where it probably terminates on the ground-bar kit on that side of the panel.
Looks like a sub-panel to me, and if this is the case, then the neutral should NOT be bonded to the enclosure.
-KB
The Following 2 Users Say Thank You to kbsparky For This Useful Post:
electures (04-10-2013), Speedy Petey (04-09-2013)
Old 04-09-2013, 09:46 PM   #9
Cletis said so.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
electures (04-10-2013), jbfan (04-09-2013), ren79eg (04-09-2013)
Old 04-09-2013, 09:46 PM   #10
Master Electrician
No bonding is allowed. Grounding electrode needed under current codes for separate structure.
Old 04-09-2013, 10:52 PM   #11
I spoke with an electrician I've used before who said that current code for detached structures requires treating it just like it's a main service panel. The actual main panel has it's own ground rods. This sub panel is fed by 4 wires as was stated. I was told that I should disconnect the 4th ground wire from the ground bar and tape it off. Then bond the neutral and ground bars and connect to the ground rods. I've done all that (although the pics don't show the ground wire disconnected).
Old 04-09-2013, 11:00 PM   #12
jbfan's Avatar
Rewards Points: 138
Time for you to find another electrician!
jbfan is online now   Reply With Quote
The Following 6 Users Say Thank You to jbfan For This Useful Post:
brric (04-09-2013), electures (04-10-2013), Jim Port (04-10-2013), mpoulton (04-10-2013), Speedy Petey (04-10-2013), stickboy1375 (04-10-2013)
Old 04-09-2013, 11:21 PM   #13
I must be missing something then because I have used this electrician for many projects (this one is my own house) and he always passes inspection, always. He did say that this is the new code in Portland, OR and sometimes even the inspectors are confused by it.
Getting back to my original question, though, where could I get that bonding screw?
Old 04-09-2013, 11:28 PM   #14
jbfan's Avatar
Rewards Points: 138
Are you feeding this from your main panel?
The code for years has been to run 4 conductors to sub panels.
If this is a detached building, then ground rods are required at the building also.
The grounds and neutrals are never boned at a subpanel, therefore, you do not need a bonding screw.
Old 04-09-2013, 11:39 PM   #15
Yes, it's being fed from the main panel. Apparently there is some discussion amongst inspectors as to the best way to do it. I have an inspector coming tomorrow for the main panel, which is done, and will just ask him. I had hoped to have it all ready but it's not being inspected yet anyway.
I'll report back what he says.
Thanks.
The Following User Says Thank You to justinae For This Useful Post:
jbfan (04-09-2013)
FPE Panel change out. Main Breaber to Lug TJ14u Electrical 4 01-22-2013 11:54 PM
Sub Panel over 10g-2 Help Needed hamblinh Electrical 30 01-18-2013 08:46 PM
Passing wire to another panel theatretch85 Electrical 5 09-21-2009 12:09 AM
Bonding Ground and Neutral matrix733 Electrical 11 11-28-2007 07:22 PM
breaker panel question chadvavra Electrical 11 08-10-2007 10:20 AM