Old 07-30-2012, 01:28 AM   #1
Thadius856's Avatar
Miscolored THHN Switch Loop Without Ground Conductor
Was helping a friend recently and he let me into a situation where a contractor had installed a 4x4 jbox to move a light switch from one wall to another, removed the old switch, and nutted the wires at the jbox. Because the contractor failed to show for several appointments, he fired him. This, he had no switch and no kitchen light.
At the jbox, he has two romex coming in. One leads upstream towards the panel, the other is coming from the light. Both 14-2. Another recep on this circuit has a two prong device that looks very old. And this is a 1940s house. I'm going to assume there's no ground continuity back to the panel as its the old woven Two wire NM at the breaker. Didn't wanna take his panel cover off if I didn't have to.
So on his own, he pulled two pieces of 14 gauge THHN down the wall to the new switch as a switch loop. The connections look fine to me, but I have three questions:
1- He couldn't get the conduit past the blocking. Is THHN without conduit in an uninsulated interior wall allowed?
2- He didn't pull a ground. Is this legal if the ground doesn't go back to the panel anyway?
3- He used red/black instead of black/black. Can it be remarked to meet code?
Northern California. Not sure if NEC 2005 or 2008 applies in his county. Ill help him pull some Romex with my cable bit and fish tape if it's unsafe.
Check out my on-going
Current Project: Whole House Data Wiring
Back Burner: Drywall Patching
Planning: Kitchen Reno
Thadius856 is offline   Reply With Quote
Old 07-30-2012, 06:44 AM   #2
1. No. The THHN wires may not pass into a gap of empty space or an unlined stud hole between where one piece of conduit leaves off and the next piece begins.
2. No, A ground wire (equipment grounding conductor) must be pulled to accompany the other wires. Exception, wires in approved metallic conduit with metal junction boxes to form a continuous path (a bonding) back to the panel for grounding purposes.
3. No remarking is needed. Red may be substituted freely for black, All colors besides green and white are for hot wires.
4. For the 2011 code and also for futureproofing, a (white) neutral also needs to be pulled.
5. It is against code to hang anything new off of a (grandfathered) circuit that does not meet code, for example a circuit that is not grounded.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded.
Changing A Double Switch to a single pole switch and a dimmer switch loydbrahn Electrical 0 11-09-2011 12:00 AM
Light switch - Taping into ground wire ok? SimpleJack Electrical 2 08-15-2011 08:04 AM
can switch work for two different outlets? jlmran Electrical 8 02-10-2011 01:31 PM
Help with 3 way switch loop wylde8 Electrical 7 12-17-2009 06:53 PM
Two ground wires for one switch, none for another? josquin Electrical 5 07-01-2007 03:31 PM