Mig Welder Connection - Electrical - DIY Chatroom Home Improvement Forum
Old 06-28-2009, 04:18 PM   #1
Saftety First!
Rewards Points: 77
Mig welder connection
I need a recept. for a mig welder.
Primary input data is: 230 vac, 22.5 amps, 60Hz.
Can I use #6 awg. with a 50 amp. recept. on a 50 amp. 2-pole breaker?
I believe I saw a post by speedy petey about this.
But I can't find it.
Or does the breaker and/or wire need to be smaller?
It will only be about a 3ft run from breaker to recept.
loyal is offline   Reply With Quote
Old 06-28-2009, 04:47 PM   #2
Electrical Contractor
kbsparky's Avatar
Does the welder have a cord on it? NEMA 6-50P plug on the end of the cord?
I'd start by matching up the cord with the appropriate receptacle.
-KB
Old 06-28-2009, 04:58 PM   #3
Saftety First!
Rewards Points: 77
Has a cord only. But it didn't come with a plug. I picked up a 50 amp. welder plug and socket from Home Depot. Can I use them?
Old 06-28-2009, 05:00 PM   #4
kbsparky's Avatar
What wire size is the cord?
-KB
Old 06-28-2009, 05:10 PM   #5
Saftety First!
Rewards Points: 77
Hard to make it out, but I think it says 12.
Here are the specs. I forgot to post.
Primary power: 230 VAC, 22.5 amp. 60Hz..
Secondary power: 30 VAC, 180 amp. 120 amps at 25% duty cycle.
Old 07-01-2009, 05:42 PM   #6
Journeyman Wireman
30 amp should be big enough. Where did you get 50 amp from?
jbberns is offline   Reply With Quote
Old 07-01-2009, 06:45 PM   #7
kbsparky's Avatar
With those specs, then you are allowed to use a 45 Amp breaker, along with a 50 Amp receptacle and cord cap.
You are allowed to set overcurrent protection at 200% of the rated primary current of the welder, with the next-larger size breaker permitted if that number does not correspond to a standard-size breaker. Since 240.6 states that 45 Amp is a standard size, then you can not utilize a 50 Amp breaker for such equipment.
But the rating of the receptacle on a 45 Amp circuit can be a 50 Amp NEMA 6-50R.
-KB
Old 07-01-2009, 07:57 PM   #8
Saftety First!
Rewards Points: 77
Thank you for the reply kbsparky.
I think I seen the 50 amp recpt. and the 50 amp breaker
on an old post from speedy. But I think now that he was
referring to to an arc welder. I have a 30amp 2 pole on hand.
I think I'll use it as you have suggested.
Thanks much
Telephone Jack Connection Problem jogan Electrical 9 04-20-2009 07:10 AM
240v Welder powered by portable generator? MRJChannahon Electrical 19 03-30-2009 06:19 PM
240v Welder powered by portable generator jackgerd Electrical 10 11-06-2008 02:38 PM
MIG welding amakarevic Tools 28 02-20-2008 09:56 PM
Miller syncrowave 250dx Welder installation saddletramp Electrical 6 01-10-2008 02:11 AM