Meter/main Combo To Load Center Grounds And Bonding? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-15-2013, 06:58 PM   #1
meter/main combo to load center grounds and bonding?
Hello People,
I have a 200 A service to a meter socket which feeds a 200 A load center through a 2" nipple. There is no "main" breaker at either side (socket or load center). The load center doesn't have room for the number of circuits I need.
My proposed upgrade will give me two main breakers so that I can disconnect either the load center or both panels. The new meter/main has 8/16 spaces/circuits and will be located outside (surface mounted) as underground feed in 3" conduit. The new load center will be flush mounted inside.
I am changing out the 200 A meter socket to a 200 A Siemens meter/main (M/M) combo, w/ feed thru lugs, (feed thru lugs at bottom of Buss controlled by the 200 A main). I intend to wire from fd. thru lugs to a Sq D load center with its own 200 A main breaker. Does this make the load center a sub-panel or since it is wired in series with the meter/main is it just an extension of the meter main as regards bonding neutrals and grounds. The installation of these two new panels will be back to back with a 2" nipple with 3/0 Cu hots and 1/0 neutral. This M/M will have a #4 Cu solid or braided wire to two grnd. rods. No attachment to water pipes as service is in PVC. I do have an CEE (concrete encased electrode or 'uffer') currently attached to my existing load center though I am uncertain of its integrity. My existing load center has the grnd , neutral and enclosure bonded together and an additional #6 solid Cu wire to a questionable grnd. rod outside below the meter socket. The existing meter socket has no dedicated ground wire, and relies on the nipple/nut for bonding to the load center and its grounds.
My confusion is regarding the proper grnding of the new (proposed) load center!
The new Sq D (QO) load center has 4 bars attached by a screw to the neutral buss, but there is no screw attaching the neutral to the enclosure (there is provision for a bonding screw to attach these neutral and ground bars to the enclosure though I don't have the screw). The label indicates that as service equipment I can attach grnd wires to unused openings in these bars, but it doesn't address whether to bond these busses to the enclosure). It seems I could remove two of these bars and attach them directly to the enclosure for grounding my circuits separate from the neutrals if that is the proper way to set this up (there are three locations in the enclosure with a single screw hole and two tits that would index with these bars presumably for attaching two of the four bars directly to the enclosure, and separate from he neutrals <or I could purchase two new grnd. bars and install there>.
Questions: For purposes of clarity; when I am talking of neutrals and grnd. buss bars I am talking of attachment points for the white commons and bare ground wires for my circuits. NOT the 3/0 neutral attaching from the pole to the meter/main to the load center.
1) Treat new load center as a sub-panel, and I believe that would mean I need to either install new grnd. bars attached to the enclosure or steal two of the four neutral/grnd. bars from the neutral/grnd bar configuration that exists?
2) Treat the new load center as an (series) extension of the meter/main combo and find a bonding screw to bond the neutral, grnd. and enclosure?
3) Can I/should I, run a #4 bare Cu wire through the nipple from the meter/main into the load center and what do I do with it (a four wire set-up)?
4) If the load center needs the neutral/grnd busses attached to the enclosure where might I find such a bonding screw (it looks to be about 1/4 inch fine thread hole in the buss bar with the hole in the enclosure not threaded, like the screw would be self-tapping)? This would presume the load center is to be treated as an extension of the service entrance.
5) If the load center is to be treated as a sub-panel, am I correct that the ground bars need to be separate from the neutrals and attached (bonded) to the enclosure?
6) When is it necessary to actually isolate the ground wires with an insulator?
7) Please provide any other questions and answers to other aspects of my proposed situation that I have missed.
Thank You for any/all input?
Timing is critical to me, but I know others have lives and priorities that are different from mine, so thanks in advance for any feedback I might get here!
ronsquery is offline   Reply With Quote
Old 03-15-2013, 07:21 PM   #2
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Originally Posted by ronsquery View Post
Hello People,
I would do all my grounding and bonding in the meter main and run four wires H H N G to the indoor panel.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 03-16-2013, 05:29 AM   #3
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Anything after the first disconnect is to be treated as a sub-panel, in your scenario, all the bonding must transpire at the Meter/Main, even though you want a disconnect at the load center, it does not change anything, the load center shall have all neutrals and grounds separate and supplied by (4) conductors.