Meter to LC, is this a Raceway?
Hi, I'm trying to understand my application as it applies to the 1-Ph 3-wire feeder wire from the meter to the load center so I can choose/determine the proper wire temperature rating for load purposes.
The two boxes are separated by a ~2" offset fitting, so if I measure from the meter lugs to the Main lugs, the total length of L1 or L2 will be about 6-ft. So when I run this wire, is the effective enclosure considered a raceway or are the conductors considered "in free air". I suspect its a raceway but I need clarification.
I'm looking at NEC-2008 Table 310.16; is this the correct table for my application?
I may need to get some 90 Deg-C wire (i.e. THW-2 or THWN-2) instead of 75 deg-C wire like THWN.
Thanks for your expert help.
Johnd85053 is offline   Reply With Quote
Old 02-06-2012, 10:13 PM   #2
Licensed electrician
Rewards Points: 1,486
Are you trying to size the conductors to feed your panel?
Old 02-06-2012, 10:15 PM   #3
Yes, exactly. Its a 200A panel.
Old 02-06-2012, 10:18 PM   #4
2/0 copper or 4/0 aluminum.
Table 310.15(B)(7) Conductor Types and Sizes for
120/240-Volt, 3-Wire, Single-Phase Dwelling Services and
Feeders. Conductor Types RHH, RHW, RHW-2, THHN,
THHW, THW, THW-2, THWN, THWN-2, XHHW,
XHHW-2, SE, USE, USE-2
Conductor (AWG or kcmil)
Service or Feeder
Rating (Amperes) Copper
Aluminum or
Copper-Clad
Aluminum
100 4 2
110 3 1
125 2 1/0
150 1 2/0
175 1/0 3/0
200 2/0 4/0
225 3/0 250
250 4/0 300
300 250 350
350 350 500
plummen (02-06-2012)
Old 02-06-2012, 10:36 PM   #5
Thanks Jim. But, does that table trump the next table "Allowable Ampacities... for no more than 3 conductors in a raceway"?
Why I ask is if I use my referenced table, and assuming I use CU 2/0 wire, the allowable ampacity is 145A/175A/195A depending on wire temp rating as opposed to your table reference which says the allowable is 200A for 2/0 wire (but fails to mention wire temperature rating!). Thus, I'm at odds with the data, seems contradicting. What am I missing?
Old 02-06-2012, 11:22 PM   #6
Semi-Pro Electro-Geek
Rewards Points: 2,922
Two reasons: Service entrance conductors are treated differently than other wiring, and also the conductor temperature ratings are often not very important because the termination ratings are usually lower. You can't use 90C wire at the 90C ampacity if you have 60C terminations.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
Johnd85053 (02-07-2012)
Old 02-07-2012, 04:03 AM   #7
You are also allowed to round up for service cables.
zappa (02-07-2012)
Old 02-07-2012, 05:22 AM   #8
Master Electrician
Rewards Points: 3,820
Is this a single phase service to a dwelling unit?
brric is online now   Reply With Quote
Old 02-07-2012, 11:31 PM   #9
Yes, this is 1-Ph to a dwelling.
mpoulton, thanks for your response, it got me thinking. I see your answer is explained by 110.14(C) which I had to re-read a few times until I really understood the issue regarding wire temperature rating and how you can manipulate the ampacities by choosing the right equipment. Checking all my equipment datasheets I find 75C is the limit at all my terminations; I couldn't use 90C wiring if I wanted to (legally). Very interesting. Again, thanks for the info.
Old 02-08-2012, 12:26 AM   #10
Julius793's Avatar
You could use 90c wiring, you just treat it as 75c for figuring the ampacity. However when derating you will have an advantage of starting at the 90c ampacity.
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Meter Main problem. right-sided meter? acerunner Electrical 6 07-23-2011 12:41 PM
320Amp double lug meter - (2) 200amp panels 1texasguy Electrical 31 07-15-2011 10:47 AM
Height of meter box Arky217 Electrical 4 05-23-2011 10:56 AM
Possible Defective or Incorrect Electrical Meter? MorganB Electrical 10 01-18-2011 09:51 AM
Water meter aggravations Ultrarunner2017 Plumbing 8 03-21-2009 06:53 AM