Meter Jumper Necessary? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-06-2008, 06:55 PM   #1
Rewards Points: 150
meter jumper necessary?
is it necessary to have a water meter jumper, or can i just attach the wire to the street side of the water line?
drewhart is offline   Reply With Quote
Old 11-06-2008, 06:59 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
A removable water meter must be jumpered around.
For reference:
250.53(D)
(1) Continuity
Continuity of the grounding path or the
bonding connection to interior piping shall not rely on water
meters or filtering devices and similar equipment.
Old 11-06-2008, 07:15 PM   #3
Rewards Points: 150
its cpv in the house. so i ran the wire all the way from the electrical box to the street side of the water line. so this is no good?
Old 11-06-2008, 08:06 PM   #4
Metallic piping systems must be bonded. If there is only a small amount of copper, if at all, after the meter then you are fine.
Old 11-06-2008, 09:22 PM   #5
Rewards Points: 150
yes there is only about six inches of copper after the meter. but like i said, the wire goes from the box all the way to other side of the meter. the street side. so no jumping is ok then?
Old 11-06-2008, 09:32 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Yep thats fine... had you connected to the house side of the meter the jumper would be required.
Old 11-06-2008, 10:09 PM   #7
Electrician
Size:  71.1 KB..............
chris75 is offline   Reply With Quote
Old 11-06-2008, 10:17 PM   #8
Rewards Points: 150
what will the city inspector say. should i attach the ground wire to six inches of copper i have on the house side of the meter, then put in a jumper to the street side? or should i just conncect the wire to the street side directly, which seems to eliminate the need for a jumper. i can see if all the pipes were copper and i attached it near the electric meter, then i would need a jumper. but in my case i dont think i need one. i just dont want the inspector to say anything.
Old 11-06-2008, 10:21 PM   #9
Electrician
IMO, you dont need the jumper. but my opinion really means nothing.
Old 11-07-2008, 12:56 AM   #10
DIYer
If you didn't bond both sides, isn't it conceivable that the inside pipes could become energized and pose a hazard?
250.104 (A) seems to say that all metal water piping and exposed structural steel "shall be bonded". What do you all think?
I think this is what Speedy was trying to say before. The point is to ground the pipes as much as it is to use the pipes as a ground.
Gigs is offline   Reply With Quote
Old 11-07-2008, 01:12 AM   #11
DIYer
Originally Posted by Stubbie View Post
His inside pipes are plastic cpvc on the house side of the meter.
Oh heh, I wondered what "cpv" was. Glad you could decipher it heh. Yeah then what I said doesn't apply at all.
Old 11-07-2008, 01:20 AM   #12
UAW SKILLED TRADES
Stubbie's Avatar
Gigs
I deleted last post as didn't like the way I worded things. But yeah I don't see a need for the jumper. But as Chris said or implied it's the inspectors opinion that counts.
Does it matter how close your panel is to your meter? jamiedolan Electrical 10 10-18-2008 04:38 AM
Clamp Meter Findings jamiedolan Electrical 16 09-08-2008 08:13 PM
Is it normal to change the upper line at the meter when running new supply line? twilightcall Plumbing 3 08-08-2008 11:10 AM
Meter ratings Stubbie Electrical 3 04-02-2008 10:12 PM
200A Upgrade - Meter Socket Location Question bjones Electrical 2 11-12-2007 03:03 PM