Meter Base And Disconnect Grounding - Electrical - DIY Chatroom Home Improvement Forum
Old 03-23-2013, 10:31 PM   #1
Rewards Points: 512
Meter Base and Disconnect Grounding
This is a 4-wire 200amp for mobile home.
Should the bare ground be ran to the ground rod from the meter, from the disconnect, or from the panel inside the home?
It IS allowed in my area to ground at the meter, but I don't see a terminal in there for the #6 Bare.
I'm using 4/0-4/0-2/0-2 AL.
Old 03-24-2013, 03:25 AM   #2
Electrical Contractor
kbsparky's Avatar
You only need 3 conductors from your meter box to the outside disconnect switch.
Bond the neutral wire there, and connect all your ground wires on the neutral bar. The 4 insulated wires to the mobile home originate from the outside disconnect switch.
IF you are required to run the ground wire from the meter, you found the terminal: The one highlighted with the green line. Otherwise, leave it empty.
I prefer to use a combo box for such installations. No need to wire up separate meter and disconnect boxes, since the one box serves as both:
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
sirsparksalot (03-24-2013)
Old 03-24-2013, 08:02 AM   #3
Rewards Points: 512
Kb, thanks.
I'm not required to run the ground to the meter, but I can, and did, so it's good to just leave it that way, I take it?
I have separate meter base and disconnect - they're back-to-back.
Old 03-24-2013, 08:12 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,968
Some areas still allow it, most prohibit it.
I'd run my grounds to the disconnect, but if your area allows it to the meter pan and it's done already, leave it.
We ran grounds to meters for a hundred years.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 03-24-2013, 08:22 AM   #5
Rewards Points: 512
Thanks guys.
Old 03-24-2013, 08:58 PM   #6
Rewards Points: 512
Hey guys,
I left the EGC connection to the meter socket, per Speedy, as it was already installed.
I'm not sure if the neutral and ground on the disco needs bonding, though, since the bond is at the meter. Thoughts?
Edited to show EGC instead of GEC
Old 03-25-2013, 03:36 AM   #7
Rewards Points: 512
Bumping:
I know it's usual to bond neutral and ground at Disconnect, but I'm not sure if it's needed with the EGC connected to the meter socket
Help?
Old 03-25-2013, 07:37 AM   #8
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
FYI - You can not enter this enclosure from behind or from the right hand side with 4/0. It can only enter from the bottem or left side.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 03-25-2013, 02:02 PM   #9
Rewards Points: 512
Article please? It's done all the time around here, as I hear
Old 03-25-2013, 02:06 PM   #10
Rewards Points: 512
BTW: here's the install
Old 03-25-2013, 06:26 PM   #11
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Why the heck is the panel so far above the top of the post? It would have looked so much cleaner if you drove two posts and installed 1x4's between the post, then mounted the equipment next to each other...
Old 03-25-2013, 07:10 PM   #12
Rewards Points: 512
Yeah, I know. I didn't measure correctly.
AND, I had already punched the KO on the meter base without realizing that I needed to punch a 2.5" hole to center the darn thing. Once I punched the KO, I didn't think I'd be able to make a different KO to center it.
Old 03-25-2013, 07:13 PM   #13
Rewards Points: 512
I passed inspection on this, but I'd still like an answer to the original: I forgot to bond the neutral and ground on the disconnect. I want to know if I should bother to go out there and bond it seeing that this is a 4-wire system AND the EGC is connected at the meter base, AND it passed inspection?
Old 03-25-2013, 07:15 PM   #14
Rewards Points: 512
IN ADDITION: Had I brought the disco down to top level, it would have made the meter below the required 3'-5' requirement, as the post is only 8'.
Old 03-25-2013, 07:24 PM   #15
E2 Electrician
So how high off the ground is the main breaker?
Main panel Bonding and grounding tulk Electrical 12 11-28-2012 10:19 PM
Section 310.15(B)(6) vs. 210.4. Don't assume, call your friendly AHJs! Daneel Electrical 3 04-11-2012 07:24 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
320 amp meter JONBOY Electrical 17 02-04-2010 06:14 PM
Question on Code w/regards to holes in Meter Bases or Panels etc. tsenator Electrical 10 10-22-2009 10:37 AM