Measuring Voltage Drop - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 04-23-2013, 07:17 PM   #16
Architectural Sculptor
RWolff's Avatar
Rewards Points: 502
Originally Posted by ddawg16 View Post
One of the ways to test how good those connections are is to do a load test. For those that don't understand...a load test is where you put a known load on a ckt and measure the voltage drop. For a given load (current), there will be a pretty accurate voltage drop down that wire.
For example....if your using 12g wire....and you have a 10a load 100' (200' of wire) from the voltage source....then, you will have an ideal 3.096 volt drop at the load. Or, if you source is 120 Vac....the voltage at the load will be 116.904 volts.
This all makes perfect sense to me and I'm not an electrical contractor. By using that method you certainly would be testing the quality of the connections as you said, what you describe is actually a pretty nifty technique.
RWolff is offline   Reply With Quote
Old 04-23-2013, 08:14 PM   #17
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
To many variables for any practical usage though...
Old 04-23-2013, 10:06 PM   #18
dmxtothemax's Avatar
Rewards Points: 5,362
It's a rough and ready approach,
But it's good enough for most layman type DIY'ers.
Electricains and engineers would be a bit more
precise and thorough due to legal liablities.
dmxtothemax is offline   Reply With Quote
The Following User Says Thank You to dmxtothemax For This Useful Post:
stickboy1375 (04-24-2013)
Old 04-24-2013, 09:19 AM   #19
Rewards Points: 150
How? This is pretty darn precise. And thorough. How would one measure voltage drop more precisely than by applying a known load and using a voltmeter?
SquishyBall is offline   Reply With Quote
Old 04-24-2013, 12:14 PM   #20
RWolff's Avatar
Rewards Points: 502
Yep, that's about as accurate as one would get, what they call real world measurements, you measure the actual physical loads on the real system running them.
I have a single phase 220v, 2 HP Century repulsion-induction motor built in 1928 in my basement of my house running an organ blower, the plate has the specs and I've put a clamp meter on it years ago to measure the amps on startup but I forget what it is was, I haven't noticed any of my lights dimming, I know it has good connections.
http://i.imgur.com/FQYM3nY.jpg
http://i.imgur.com/vWoROWp.jpg
As ddawg16 said earlier but in different words- putting a known load on and measuring the drop:
Old 04-25-2013, 12:44 AM   #21
JOATMON
ddawg16's Avatar
Rewards Points: 1,826
It's nice to see that a few people 'get it'....
I put the method to work this evening....in the process of removing part of a wall over the weekend, my sawzall (me) cut a piece of existing NM cable by accident...so this evening I climbed up into the attic...pulled the damaged piece up...stuck it in a box...ran a new piece down....wire nutted everything......4.2v drop through about 70' (140') of wire at the furthest point.
So....I have a slightly higher voltage drop than I should have...it should be around 2.2 volts.....that means I'm dropping about 20w at one or more connections. It could be the outlet....it could be one of my connections. Part of my problem is that the back half of this ckt is the 60 year old part of the house....and I know that at least 2-3 of the outlets are wired using the outlet as the junction instead of using a pig tail.
20w is not much....but....if I'm using a slightly higher load...say a crock pot that is going to be on for hours...that 20w could produce enough local heating that it starts to degrade the connection....which causes more loss....and more heat....and more loss....and more heat....and....more problems.
This weekend I'll make some mid ckt measurements to isolate the location of the high loss.
Old 04-25-2013, 04:59 AM   #22
20w loss over 70' is not too serious,
provided its equally dropped over the entire 70'.
thats about 300 milli watts per foot.
Old 04-25-2013, 08:29 AM   #23
Rewards Points: 83
If you are using a calculated IR drop based on published numbers for a given wire size ( instead of actually measuring the resistance of the wire) and you are using the nameplate specs on the device (instead of actually measuring the current draw) then a lot of your calculations of what the "voltage drop" should be may be theoretical instead of actual. You are probably using the DC wire resistance from some chart. The exact resistance is slightly greater with AC than it is with DC. Also, the exact resistance will vary with temperature. These are the type of variables that I referred to in an earlier post.
davido30093 is offline   Reply With Quote
Voltage drop? Lights dim with load on different circuit. nezwick Electrical 28 08-14-2012 10:18 AM
Voltage drop jsellers224 Electrical 15 04-17-2009 11:16 AM
2 - 900w tansformers on a 15A circuit? tonyBagadonuts Electrical 19 07-20-2008 07:15 PM
Will splice cause voltage drop? JPsAlias Electrical 6 05-19-2008 07:09 PM
Voltage Drop between switch and fixtures CaptMike Electrical 1 06-24-2005 09:30 PM