-   -   Measuring 240v, 4 wire curcuit? (http://www.diychatroom.com/f18/measuring-240v-4-wire-curcuit-173920/)
jclee 03-08-2013 12:39 PM
Can I measure 240v on my meter? I can only get 120v, however, I do get 120 from each hot wire. I'm thinking this is right?
rjniles 03-08-2013 12:44 PM
If you are measuring 120 from each hot to ground or neutral, but not 240 across the 2 hots, you have a problem.
The circuit is wired wrong or one leg is open and you are measing one side back thru the load.
jclee 03-08-2013 12:49 PM
I'm getting 120v from black to ground/neural and 120v from red to ground/neutral
I have not measured between black and red. I didn't think you could measure 2 hots together
Speedy Petey 03-08-2013 12:59 PM
THAT is your 240V.
rjniles 03-08-2013 04:15 PM
As Speedy says, that is the only way you will measure 240.
dmxtothemax 03-08-2013 04:17 PM
If both phases originate from the one hot line,
then you will measure nothing or close to it !
But if they come from different hot lines,
then you will measure 220 - 240v.
So yes you can measure across two hot lines !
Be very carefull, the mother of all bites awaits the unwary !
Death shortly after.
*CAUTION*