Max Size Wire For For Service Drop Conduit? - Electrical - DIY Chatroom Home Improvement Forum
Old 08-22-2011, 11:54 AM   #1
Max size wire for for service drop conduit?
I have searched this forum and done my best interpreting the most recent California Electrical Code but I still have questions. I want to upgrade my main service from 100 to 200amps - pretty basic. I do not want to replace the conduit that runs in the wall from the meter to the roof masthead for the service connection. It is 1 1/4" diameter EMT. My research leads me to conclude that I need 2/0 copper and it may or may not fit in the conduit according to fill charts depending on the type of insulation. What types of insulation may I use in CA in EMT for Service drop? Is it OK to provide copper even though the power company's service lateral is Aluminum?
As a side question, why in the world are you allowed to fill the conduit more if you are using more than 2 wires?!
Thank you all!
Justine is offline   Reply With Quote
Old 08-22-2011, 12:29 PM   #2
Code05's Avatar
Rewards Points: 1,104
2/0 copper is correct, but you are not gonna get it into a 1 1/4" conduit.
Fill ratio is also based on what is called "jam effect".
Code05 is offline   Reply With Quote
Old 08-22-2011, 03:00 PM   #3
Rewards Points: 330
need 1 1/2 for 3 #2/0.nec chapter 9 table 4,table 5.do thse calcs from there.the sq in of 2/0 thwn is .2223.you need 3 wires multiply by 3 gets .6669.1 1/2 emt is .814 for over two wires.so 1 1/2 is what you need.learn to0 use tables in the book.article 310 is for ampacity of conductors.
oleguy74 is offline   Reply With Quote
Old 08-22-2011, 03:48 PM   #4
Code05's Avatar
Or you can do it the easy way and use Annex C.
Old 08-22-2011, 04:05 PM   #5
Rewards Points: 330
until you have wires of different size.then you need to calculate.example,3 #2/0 and one #4.would still be 1 1/2 but you don't know till you calc.just sayin...
The Following User Says Thank You to oleguy74 For This Useful Post:
Code05 (08-22-2011)
Old 08-22-2011, 04:31 PM   #6
Code05's Avatar
I was just teasing.
Old 08-22-2011, 04:33 PM   #7
Rewards Points: 330
right on.just onfo to help the OP.since he is looking in the book.....might as well look at it all...
Code05 (08-22-2011)
Old 08-23-2011, 09:55 PM   #8
Well thanks very much, I appreciate instruction on how to properly use the tables. I see I was looking at the wrong column in the fill charts - duhh!
I also see that one of my original questions still applies: what insulation types must I use in this application since I would like to maximize my service without replacing conduit? (My other option would be to run new conduit outside the wall - but it doesn't look so nice).
Old 08-23-2011, 10:34 PM   #9
Code05's Avatar
THWN, RHW, and XHHW are common.
Ground Wire Size Question Suprageezer Electrical 12 07-28-2011 03:00 PM
What size ground wire should I use for 8 gauge power dxmullin Electrical 1 07-06-2011 02:57 PM
is UG conduit size change legal? krazni Electrical 1 07-13-2010 02:17 PM
Sub-Panel Wire Size and Conduit Questions Tmb9862 Electrical 3 12-02-2009 11:48 PM
Size of Wire & type of wire agman Electrical 6 11-10-2009 08:13 PM