Max # Service Drops - Electrical - DIY Chatroom Home Improvement Forum
Old 06-08-2014, 04:38 PM   #1
Rewards Points: 455
Max # Service drops
If I run a bunch of 100 amp #2 SEU service wires from meters up to the drop, is there a maximum amount I can run ? 5, 10, 15, 20,40 etc... ? I can't seem to locate anything yet in the NEC book
Don't want to do a meterbank if that's what your thinking...
Cletis is offline   Reply With Quote
Old 06-08-2014, 04:55 PM   #2
Idiot Emeritus
Rewards Points: 1,492
230.40 Each service drop or lateral shall supply only one set of service entrance conductors.
There are several exceptions, mostly pertaining to multiple meters and buildings.
If you're referring to parallel conductors, 310.4 states that they need to be 1/0 or larger.
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
Jump-start (06-12-2014)
Old 06-09-2014, 08:21 AM   #3
Rewards Points: 3,396
And possibly who you know
ritelec is offline   Reply With Quote
Old 06-10-2014, 06:23 AM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Not DIY.
The Following User Says Thank You to k_buz For This Useful Post:
danpik (06-10-2014)
Old 06-10-2014, 03:36 PM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
Originally Posted by k_buz View Post
Not DIY.
But Cletis is a pro
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 06-10-2014, 06:11 PM   #6
Rewards Points: 455
Well, I was just thinking... This was a 16 unit apt building so I could just basically run 16- 100 amp services all independant but tied at drop. Basically, the same. Here is my cost
100 amp service with 15 ft #2 SEU (includes meter, hub, connector, straps, seu)
$ 55 per so $55 x 16 = $ 880 total
If I did a 16 gang metebank i'm sure it would be double to triple
Thoughts ??
Old 06-10-2014, 06:21 PM   #7
A "Handy Husband"
rjniles's Avatar
It sure will look pretty
Old 06-11-2014, 12:49 AM   #8
dmxtothemax's Avatar
Rewards Points: 5,360
How the hell will you tie 16 x #2 cables together !
One big ass wire nut ?
Buss bar and wire lugs ?
Where can I get a 1600A panel from ?
dmxtothemax is online now   Reply With Quote
Old 06-11-2014, 06:11 AM   #9
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Thoughts ??
I've seen it done, it's an apartment building, so aesthetics only weigh so much IMO....
As a side note, the labor may offset the difference of just mounting ONE 16 gang meter bank vs, 16 meter sockets...
Old 06-11-2014, 06:13 AM   #10
E2 Electrician
That's the Power Company's issue, i've seen multiple service drops just bugged to a piece of copper then bugged to the POCO's supply.
Not sure what you are talking about with a 1600A panel? Cletus wants (16) 100amp panels, the calculated load is going to way less than that.
Old 06-11-2014, 08:39 AM   #11
Master Electrician
Rewards Points: 3,870
Don't forget the main disco ahead meter pack(more than six throws) or the 32 ground rods for your original idea.
brric is offline   Reply With Quote
Old 06-11-2014, 07:37 PM   #12
k_buz's Avatar
Two rods...16 connections to each rod.
Old 06-11-2014, 08:19 PM   #13
to one ?
One jumper between the two.
Old 06-11-2014, 09:35 PM   #14
Rewards Points: 1,192
Cletis,sounds like good plan. Do it and let me know how the power provider likes it.
bobelectric is offline   Reply With Quote
Old 06-12-2014, 01:30 AM   #15
Contractor in PA
With that many loads, you will definitely need a fire switch (main service disconnect). Besides not passing electrical inspection, the power utility would never energize the service or accept it.
There is also a necessity to calculate the connected load and allow for a de-rating factor.
First and foremost, I would call the electrical inspector that you intend to use and ask him what he will want installed. You probably will also need to file a S&M (service & meter) request with the power utility.
This is no small job! The property owner should understand that there are inspection and permit requirements and you must follow the code. Please don't be a penny wise and a dollar foolish. If the owner can not or will not pay to have the job done safely and correctly, walk away from the job. There is too much at stake here. (property and lives are depending on a safe and compliant installation).
michaelpwalton1 is offline   Reply With Quote
Moving electric service entrance to detached garage WillK Electrical 7 10-05-2011 10:13 PM
rewire and new service entrance wire dghowery Electrical 4 10-13-2010 08:31 AM
"Moving" service entrance WillK Electrical 4 09-29-2010 01:04 PM
How to tell Service amperage?? Buckley Electrical 2 06-06-2009 05:42 PM
How can I determine service amperage? dawho1 Electrical 13 04-07-2008 10:10 AM