Max HVAC Breaker Size - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-18-2014, 11:33 AM   #16
Master Electrician
Rewards Points: 3,698
Originally Posted by Stubbie View Post
Not the proper procedure for determining branch circuit conductor sizing and opcd to a single residential ac unit.
Never said it did. IMO there is no way the circuit described by the OP should be supplied by a 40 amp breaker regardless of whether the disco is fused or not.
brric is offline   Reply With Quote
Old 07-18-2014, 11:42 AM   #17
Rewards Points: 455
Think of it this way,
What if I ran a 240V branch cir with #10 thhn in conduit to an outdoor 3r subpanel and then put 30amp fuses or breakers to the A/C unit. Would that be ok?? If so, whats the difference in that v.s. the original case ?
Cletis is offline   Reply With Quote
Old 07-18-2014, 11:54 AM   #18
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
We actually don't know how this unit should be supplied since we do not have the information. The OP's suggestion of how he is going to do it is incorrect .
You made a statement how "some" people would look at the ops method. I was simply stating that what you wrote is not how you would approach the installation.
So what was your purpose in stating something that is incorrect ?
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 07-18-2014, 12:03 PM   #19
Electrical Contractor
jbfan's Avatar
Rewards Points: 152
The difference between the 30 amp and 40 amp breaker in the main.
Old 07-18-2014, 12:06 PM   #20
UAW SKILLED TRADES
Stubbie's Avatar
That would be feeder conductors not branch circuit conductors to the subpanel. As long as these conductors are sized to the calculated load of the panel it would be fine and of course the correct ocpd protecting them.. This is assuming your sizing the ac correctly.
Note you would probably run 120/240 circuit to the subpanel.....
Stubbie
Old 07-18-2014, 12:40 PM   #21
Master Electrician
We have the information in post #4, 30 amps max. What I said is that some would interpret the installation differently as they (not necessarily me) would say the conductors to the disco are feeders rather than branch circuit conductors as by definition the branch circuit conductors would be those from the load side of the disco to the unit.
The Following 2 Users Say Thank You to brric For This Useful Post:
electures (07-18-2014), Stubbie (07-18-2014)
Old 07-18-2014, 12:45 PM   #22
Master Electrician
Originally Posted by JohnDS
Thanks guys.
Iwire, you have raised another question. In this case, Why does installing a fused disconnect as opposed to a non-fused disconnect determine that the wire from disconnect to panel be upsized to 8awg?
Sent from my SGH-T999 using Tapatalk
By definition the conductors between the panel and the fused disconnect are feeder conductors. They would have different rules than the branch circuit conductors between the fused disco and the unit.
There has been some argument that the fuses could be supplemental protection and therefore the conductors would not be feeder conductors.
The Following User Says Thank You to brric For This Useful Post:
Old 07-18-2014, 01:39 PM   #23
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Some would say the fuses at the disco make the conductors supplying the disco feeders. Thus limiting the OCPD to 30 amps.
Bingo. Since the disco is fused the conductors supplying it are feeders. Have to protect them at their rated amps cities. #10 romex = 30A. #10 THHN = 35A.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 07-18-2014, 01:40 PM   #24
electures's Avatar
They are not branch circuit conductors to the fused disco. They are feeders.
The Following User Says Thank You to electures For This Useful Post:
brric (07-18-2014)
Old 07-18-2014, 03:41 PM   #25
An old Tradesmen
Rewards Points: 6,148
Originally Posted by stickboy1375 View Post
We are talking AC units here, In most cases, you will have a much higher rated breaker than the actual wiring is rated for, this is because the breaker is NOT protecting the wire, the AC unit is... It is not out of the norm to have a #10 AWG protected by a 50 amp breaker, but you have to go off the AC nameplate, the manufacture already did all of the required calculations for you.
The A/C is not protecting the wires.
Old 07-18-2014, 06:11 PM   #26
Master Electrician
The AC provides the overload protection.
Old 07-18-2014, 06:24 PM   #27
An old Tradesmen
Only for the condenser fan motor and compressor.
Their internal over loads only open between their common winding and their run and start windings. A partial short to ground can still occur before the internal over load.
Yes, I know the NEC feels its enough protection for the wire.
Old 07-18-2014, 06:27 PM   #28
Rewards Points: 774
Yo. If I run #10 Thhn in conduit to an A/C disconnect and fuse it with a 40 amp 2 pole hacr breaker and 30 amp fuses in disconnect will this pass NEC code?
Thanks in advance
Cletis what are you doing? I mean really!!!!
Know A Little is offline   Reply With Quote
Old 07-18-2014, 08:55 PM   #29
Rewards Points: 1,832
You guys are falling for this
Jump-start is offline   Reply With Quote
Old 07-18-2014, 09:09 PM   #30
electures's Avatar
Where did he go anyway?
Breaker & wire size rcassidy Electrical 9 05-07-2013 12:51 PM
100 Amps Breaker wire size? daythunder Electrical 6 06-07-2012 07:50 PM
Breaker is not the same size as noted on plate on ac, tripping breaker, thoughts? detyianni HVAC 13 06-10-2011 12:08 AM
What size breaker Ineedhelp2009 Electrical 7 05-20-2009 07:44 PM