Old 10-29-2011, 08:35 AM   #1
Material to wire 220 circuit
Hi,
I have two spare breaker slots in main 200 amp panel and easy access to it. I plan to wire a circuit for a saw. 3 HP motor,single phase, 18 amps. The wire run is 25 feet. Live in central Ky. Need to know wire size and breaker size. Thanks for your thoughts and answers.
vhuffines is offline   Reply With Quote
Old 10-29-2011, 09:09 AM   #2
Electrical Contractor
General rule for motor conductor sizing is 125% of the full load current plus anything else like an inspection light. You'll probably want to run #10 and put it on a 2pole 25A or 30A breaker.
Sine is offline   Reply With Quote
Old 10-29-2011, 09:10 AM   #3
iminaquagmire's Avatar
18A seems like a lot for a 3hp motor at 240v. That would be a pretty ineffient motor. Are you sure about the amperage? That would be about right for the motor if it was wired at 120v. But if it is right, wire size for this would be #10 on a 30A breaker. Your local codes may vary however especially in regards to the wiring methods allowed (i.e. conduit vs romex or AC/MC).
iminaquagmire is offline   Reply With Quote
Old 10-29-2011, 07:54 PM   #4
Thank you guys for your information. I think I will wire with#10 to 30amps.
Vernon
Old 10-29-2011, 08:31 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Your numbers are WAY off.
I'd guess it is a REAL 3HP motor, as opposed to something like a Craftsman "6hp" vacuum cleaner that only draws 15A @ 120v.
18A is pretty much dead on.
Check the tables at the end of Art. 430.
240v conduit with different gauge wires... Biospot Electrical 7 12-14-2010 08:07 PM
Burned wire coming from circuit breaker rdmirando Electrical 5 11-01-2010 06:32 PM
change wire size in a circuit? mtmisfit Electrical 2 10-17-2010 02:07 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 05:02 PM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 09:09 PM