Master Bath Wiring Help - Electrical - DIY Chatroom Home Improvement Forum
Old 08-17-2009, 11:02 AM   #1
Rewards Points: 109
Master Bath wiring help
We are remodeling the master bath, which was completely gutted and all of the old wiring was removed. I ran 2 new 12/2 wires from the main panel which will go on their own 20A breakers. My intention was to use one for outlets and the other for electric floor heat. I also ran a new 6/2 wire for steam shower generator. All new wires are not yet hooked up at the panel and I am planning on hiring an electrician for that portion.
Existing wires which were fed back into the bath are
20A GFCI breaker 10/2 for the whirlpool
Two 20A breakers 12/3 wire - This is the one I was planning on using for the lights, although I didn't realize it was what I guess is called a branch circuit.
Questions:
1. The two existing 20A breakers can be swiched separately. I think this is now against code. How do I fix that?
2. Once and if the breakers are fixed, can I use that 12/3 wire for general bathroom lighting and if so, what do I do with the extra wire/circuit? Can I just cap it in the J-box (It will not have drywall over it)
3. If I can use 12/3, and should also the other side of the circuit, can/should I wire exhaust fans to it?
4. I need to wire lights in the shower, above the vanity, and above the tub. My understanding is that they need to be on GFCI. Can I wire them to the GFCI receptacle circuit?
The pic below shows the two J-boxes where I brought power into the room. The thick cable on the right is the steam shower geerator wire
BimmerRacer is offline   Reply With Quote
Old 08-17-2009, 11:25 AM   #2
joed's Avatar
Rewards Points: 11,964
You CAN NOT 14/2 wire for 20 amp circuit.
Use the 12/3 on a double pole breaker (not a mini or tandem) or get a handle tie to lock the two existing breakers together as one to supply the power for the light and receptacles(2 circuits). This is called a multiwire branch circuit.
You can install the fans on either lighting or receptacle circuit.
The light over the tub must be GFCI. The others over the vanity are not required to be but can be. I don't recommend it because if you trip the GFCI the light will be out if you do. They can be wired off the LOAD side of the receptacle.
Old 08-17-2009, 11:27 AM   #3
Rewards Points: 109
Sorry, typed it wrong. They are 12/2 wires, the yellow ones in the picture above
So, would this be to code?
new master bath questions jdix Plumbing 2 04-09-2009 07:07 PM
Bath remodel wiring Nhrafan Electrical 14 03-23-2007 06:53 PM
Turning a Guest Bedroom into a Master Bath BbAaSsSs Remodeling 18 03-10-2007 06:03 PM
Advice on Converting Master Closet to 3/4 Bath Thirdeye Remodeling 9 02-13-2007 08:37 PM
electrical wiring in bath. pinman52 Electrical 4 05-04-2006 07:01 AM