Main Vs Sub-panels - Electrical - DIY Chatroom Home Improvement Forum
Old 06-06-2008, 10:44 AM   #1
Main vs Sub-panels
Hi,
I have a "main panel" on the inside wall of my garage with no main circuit breaker connected through the wall to an outside box that houses the main breaker (just through the wall and below the inside box). The inside panel is wired as a main service panel (neutral bar bonded to box and ground bar connected to the neutral bar). Why is this inside panel not considered a sub-panel and wired with the neutral and ground bars separated?
Thanks! Brad
bradoflv is offline   Reply With Quote
Old 06-06-2008, 11:02 AM   #2
Rewards Points: 270
Is the outside panel a panel with branch circuits, or just a box housing a single main breaker?
pcampbell is offline   Reply With Quote
Old 06-06-2008, 11:09 AM   #3
main vs sub panel
the outside panel is strictly a main breaker, nothing else.
Thanks!
Old 06-06-2008, 11:43 AM   #4
joed's Avatar
Rewards Points: 11,506
It should be wired as sub panel.
Where does the main ground conductor enter? The main disconnect? or the panel? Normally the ground should enter the main disconnect and a four wire feeder to the panel.
Old 06-06-2008, 11:43 AM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
That should NOT be wired this way. Even though this is your service panel, there should be NO neutral bond.
Old 06-06-2008, 12:58 PM   #6
Registered User
Termite's Avatar
Agreed, it is wrong. The "point of service" is that main breaker. That's where your grounding electrode conductors should originate from, and that's where the bonding should occur. Neutrals should definately float in the interior panel, which is a sub-panel, even though it is the only panel you have.
Old 06-06-2008, 01:28 PM   #7
Rewards Points: 58
I am seeing many people using combo meter/load center enclosures. In each and every case all subsequent panels connected to this type of service panel will be considered sub panels.
I have become very fond of these type service panels as you can use lug panels inside and out. Plus they have the capability of a few breaker slots in them that can be used for anything you like. Great for pools spas, and detached structures ect....
J. V. is online now   Reply With Quote
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Replace main panel? And lots of other ?s Bcoleman6 Electrical 13 01-22-2008 10:40 AM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 09:18 PM
Arced main lug in service panel burgeke Electrical 4 11-02-2006 12:28 PM