COLDIRON 08-19-2011 06:55 AM
Main service panels
Main Panels are they both legal according to NEC.?
1. Main Service Panel 100,200 amps
2. Main Service Panel lug 100, 200 amps
Both with proper circuit breakers .
CheapCharlie 08-19-2011 06:59 AM
Not exactly sure what you're looking for here. More info?
brric 08-19-2011 07:05 AM
Because I am both psychic AND I can read your mind I will say, yes.
rjniles 08-19-2011 07:08 AM
Used in the correct application, any of the those items would be compliant.
COLDIRON 08-20-2011 12:15 PM
More info on the panels
Main service panel looking at it has a main breaker installed up top that says main and turns on and off up and down position.
Main lug panel has busses with lugs and a breaker is added at the top with sideways action.
Originally Posted by rjniles (Post 710643)
used in the correct application, any of the those items would be compliant.
thanks
rjniles 08-20-2011 12:31 PM
This describes a main lug panel with a breaker (back-fed) to provide a disconnect. You do not need a breaker installed in a main lug panel to use it as a service panel. The disconnect breaker can be installed remote from the panel and the feeder connected directly to the panel main lugs. A very common installation scenario.