Old 07-19-2012, 12:09 PM   #31
Originally Posted by mpoulton View Post
Yes, that is normal. Those wires coming into the main breaker are from the utility, and there is no way to shut them off.
So, you are saying that voltage between the two green dots in the attached picture should be 120v, with the breaker off? Correct?
Not likely. As we said before, the current on your neutral is probably not from your service. It's from a neighbor's service, and it's coming in through your plumbing and leaving through your utility neutral connection. Check the current on the plumbing bonding conductor or your incoming water main. It's probably the same as the current on the neutral with the main breaker off.
Would this extra currect cause my meter to "turn" (it is one of the new digital meters and hard to tell if it is actually "turning")
Fisher252 is offline   Reply With Quote
Old 07-19-2012, 12:29 PM   #32
Electrical Contractor
jbfan's Avatar
Rewards Points: 252
The 2 green dots should show zero voltage.
Did you measure current from the top of the main breaker with the power off?
Did you check voltage from ground and neutral from the bottom of the breaker with the main off?
Have you checked your meter to see if it has any movement with the main off?
Old 07-19-2012, 12:43 PM   #33
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If he used a wiggy he might be showing voltage because of a light bulb installed and turned on.
The Following User Says Thank You to k_buz For This Useful Post:
jbfan (07-19-2012)
Old 07-19-2012, 12:49 PM   #34
jrclen's Avatar
Rewards Points: 514
With the breaker on. With the breaker off it should show 120 volts.
Fisher, you need the power company and or an electrician. This is nothing you are going to fix yourself. And it needs to be fixed. Start with the power company, they are free.
John
jrclen is offline   Reply With Quote
The Following User Says Thank You to jrclen For This Useful Post:
mpoulton (07-19-2012)
Old 07-19-2012, 02:07 PM   #35
Semi-Pro Electro-Geek
Rewards Points: 2,902
The voltage between the green dots is not a relevant measurement. With the main breaker on, it will be zero. With the main breaker off, it will probably be around 120 but might not be. It doesn't matter. The current through your neutral will not affect your power bill, since it doesn't pass through the meter. The problem is not in your house and there's nothing you can do to fix it. Only the power company can do it. You need to contact them and have them fix your neighbor's service neutral.
mpoulton is offline   Reply With Quote
Old 07-19-2012, 04:42 PM   #36
jrclen's Avatar
Rewards Points: 514
The voltage across a switch or circuit breaker or fuse is certainly relevant when trouble shooting. Seeing voltage tells us the device is open. Not seeing voltage tells us the device is closed. Reading zero volts across a breaker which is supposedly turned off indicates a problem. Or tells us the power is off.
John
Old 07-19-2012, 05:52 PM   #37
Ok, good. That is how it is.
I will give the POCO a call next week.
Old 07-19-2012, 06:27 PM   #38
k_buz's Avatar
Next week? man, call them now!
Old 07-20-2012, 12:03 AM   #39
Of course it's relevant to troubleshooting some problems, just not this one. He already knows the power is off.
Old 07-20-2012, 08:50 AM   #40
jrclen's Avatar
Rewards Points: 514
Very common last words before meeting St Peter.
John
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM
new sub panel BlueBSH Electrical 11 01-22-2012 09:28 AM
Fuse panel main breaker question cjm94 Electrical 5 11-16-2011 10:16 AM
Subpanel next to Main panel wired the same in 1990 Uncle Wayne Electrical 3 01-20-2011 01:43 AM
GFCI feeing subpanel question scott2332 Electrical 45 02-28-2009 04:15 PM