Main Neutral Is Breaker Panel Question - Electrical - DIY Chatroom Home Improvement Forum
Old 07-13-2012, 04:34 PM   #1
Main Neutral in Breaker Panel Question
The main neutral wire coming into the breaker panel reads 5 Amps even when the main breaker is off. What could be causeing this?
Fisher252 is offline   Reply With Quote
Old 07-13-2012, 04:39 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 464
5 amps or 5 volts?
Old 07-13-2012, 04:45 PM   #3
Amps ..
Old 07-13-2012, 04:46 PM   #4
Civil Engineer
Rewards Points: 4,764
Exactly how are you measuring the 5 amps?
Old 07-13-2012, 04:52 PM   #5
clamp on amp meter
Old 07-13-2012, 05:00 PM   #6
jbfan's Avatar
Rewards Points: 464
If you have current, then you have voltage.
Check each leg of the main breaker.
You could have a bad main.
Old 07-13-2012, 05:43 PM   #7
I flipped all of the breakers to off and still the 5 Amps...
Old 07-13-2012, 05:47 PM   #8
jbfan's Avatar
Rewards Points: 464
Did you check the main for amperage?
Is your meter turning?
With the main breaker off, did you measure any voltage?
The Following User Says Thank You to jbfan For This Useful Post:
Missouri Bound (07-13-2012)
Old 07-13-2012, 05:56 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Clamp your water pipe bonding wire or any of your grounding electrode conductors in the panel (be careful) .. do you show 5 amps total between them or any one of them?
The Following User Says Thank You to Stubbie For This Useful Post:
andrew79 (07-13-2012)
Old 07-13-2012, 07:10 PM   #10
PM me for a method to trace this down.
Old 07-13-2012, 07:50 PM   #11
Missouri Bound's Avatar
Test your ammeter on a known value. Amps is a measurement of current and it's not there unless voltage is present. Check the voltage at the mains. 5 volts with a digital meter wouln't be odd. Check for voltage with a wiggy or the like.
Do you want it your way or the right way?
Old 07-13-2012, 08:12 PM   #12
Master Electrician
Originally Posted by Yoyizit View Post
Assuming the resistance of a chunk of earth is 25 ohms, one way to do this would be to have the PoCo transformer center tap and the ground connection at your house be at a potential difference of 5A x 25 ohms = 125v.
If you go with 5 ohms for the resistance of the volume of earth then it's 5A x 5 ohms = 25v.
Sandy soil has high resistivity and clay has low, and moisture will lower the resistivity. Which do you have?
this guy makes me giggle all the time. Also makes me not regret saying no to drugs.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
The Following 4 Users Say Thank You to andrew79 For This Useful Post:
jbfan (07-13-2012), Speedy Petey (07-15-2012), stickboy1375 (07-15-2012), Yoyizit (07-14-2012)
Old 07-13-2012, 08:32 PM   #13
...and makes me wish I had.
The Following 2 Users Say Thank You to Missouri Bound For This Useful Post:
Speedy Petey (07-15-2012), Yoyizit (07-14-2012)
Old 07-15-2012, 03:37 AM   #14
Semi-Pro Electro-Geek
Rewards Points: 2,938
May be a neighbor with a bad neutral connection, returning neutral current through your water or gas pipes. Check current on the water bonding conductor - I bet it's the same as the neutral current with the main off. Definitely notify the power company.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
Old 07-15-2012, 09:03 AM   #15
If there is only 5vac driving this current through the ground due to a neighborhood neutral imbalance , it's not so bad.
If it's a few hundred volts through high ground resistance, that is dangerous.
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
new sub panel BlueBSH Electrical 11 01-22-2012 08:28 AM
Fuse panel main breaker question cjm94 Electrical 5 11-16-2011 09:16 AM
Subpanel next to Main panel wired the same in 1990 Uncle Wayne Electrical 3 01-20-2011 12:43 AM
GFCI feeing subpanel question scott2332 Electrical 45 02-28-2009 03:15 PM