Main Lug Panel At Service Entrance - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-11-2010, 06:14 PM   #16
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
Originally Posted by mud99 View Post
So would it be up to code for me to add another 100 amp breaker for another subpanel to this? Because that would bring me up to about 230 amps potential fault current, which IMO does not sound "slightly" oversized anymore.
Counting up the breaker numbers is completely meaningless, regardless of what the general public might think.
This is a case of 100 + 30 NOT equaling 130.
There used to be a type of panel called a "split-buss" panel. There were four or six main breakers. Typically a 2p50 for the range and lighting main. Ten assorted other 2p breakers for the other "mains". 100A was a typical size. If you counted up all the mains you'd often get over 200A. Again, a meaningless number.
A standard electric water heater is typically on a 2p30A breaker. This appliance will never see over 19A in use.
Understand?
Speedy Petey is online now   Reply With Quote
Old 12-11-2010, 06:23 PM   #17
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Originally Posted by emolatur View Post
I don't see very many >100A breakers that fit a QO bus. Having only two slots that accept breakers that are only available up to 100A tends to inherently limit the load to 200A.
there are 2 pole qo breakers up to 200 amp.
Termination of neutral in main service panel Mike2401 Electrical 6 09-10-2010 10:45 AM
Main panel or sub panel? tbeaulieu Electrical 5 04-07-2010 12:58 PM
Replacing 2 Sub Panels with 1 Larger Panel GuitarJack Electrical 7 08-25-2009 09:43 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 12:33 PM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 09:18 PM