12-09-2010, 07:17 PM
#1
Main Lug Panel at Service Entrance
My house was built in 1973, and has 100 amp service from the utility company.
At the service entrance, I have a meter, which then connects to a main lug QO panel. Their is no main breaker.
The main lug panel has two breakers, a 100 amp for the house, and a 30 amp for the pool equipment.
Is this allowed now/has it ever been allowed? It seems like I could put 130 amps of load onto the 100 amp utility lines, which would only be proper if they had 100 amp protection upstream, which from my limited understand they do not have.
Mark
Reason: spelling
12-09-2010, 07:33 PM
#2
Master Electrician
Where are the rest of the breakers for the house?
12-09-2010, 07:36 PM
#3
On subpanels fed from either the 100 amp or 30 amp breakers mentioned above.
12-09-2010, 08:04 PM
#4
" Euro " electrician
Do you have all in one meter socket or have two seperated box next to the meter ??
And where ya located ? { once I know which state we will figure it out pretty fast}
Merci.
Marc
12-09-2010, 08:37 PM
#5
You talking to me?
you might check to see if the 100 amp breaker is back feeding that panel and the lug connections actually feed the panel in the house.
12-09-2010, 08:50 PM
#6
Master Electrician
Legal if there are 6 or fewer breakers in that panel.
12-09-2010, 09:26 PM
#7
I'm in California, it's an all-in-one panel with the meter panel on the left and a QO load center on the right
Backfeeding from the 100 amp breaker to the main lugs is a possibility, I will have to check that. Would be totally stupid and unintuitive if someone did that, but I suppose it's technically safe, except for the fact it isn't tagged and it isn't intuitive.
12-09-2010, 10:20 PM
#8
You talking to me?
why? That allows for a single main breaker and is actually a very common installation.
your main disconnect must be labeled. If it is the 100 amp back fed, it must be labeled. If it is the two breakers, they both must be labeled.
12-10-2010, 10:40 AM
#9
I just checked - the panel is not being backfed through the 100 amp breaker.
Here is a pic of the install. The 30A breaker on left is for the pool subpanel, the 100A breaker at right is for the inside panel.
No main breaker.
12-10-2010, 10:42 AM
#10
I guess I shouldn't have called this a "main lug" panel, since their are no lugs, I was describing it from memory.
12-10-2010, 11:46 AM
#11
Electrical Contractor
Very common setup even today.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
12-10-2010, 11:57 AM
#12
You talking to me?
yes, there is a main breaker, or more correctly, 2 main breakers. That is a meter main combo. Very different than a separate MLO panel.
so, to your question: yes, theoretically you could draw 130 amps through the meter and service drop wiring. Realistically, it will never happen. Especially in a residential situation, you rarely fully tax a service. In fact, the service drop wiring is allowed to be slightly undersized because of that.
12-10-2010, 01:08 PM
#13
Can't believe this is allowed, it seems wrong. Just because most people don't fully tax their service doesn't mean it should be undersized.
So would it be up to code for me to add another 100 amp breaker for another subpanel to this? Because that would bring me up to about 230 amps potential fault current, which IMO does not sound "slightly" oversized anymore.
12-10-2010, 03:47 PM
#14
You talking to me?
I'm not seeing where you could add another breaker.
Does the literature on the cover give any limitations as to quantity and ampacity of breakers?
12-11-2010, 05:50 PM
#15
Read the labels.
Probably a 200A meter main.
I don't see very many >100A breakers that fit a QO bus. Having only two slots that accept breakers that are only available up to 100A tends to inherently limit the load to 200A.
As far as never really taxing a service entrance... that's generally true, but I had to heat the 2-story 4-bedroom project project house with electricity for a couple days (ran out of oil at a very inconvenient time) and did manage to come close - electric oven, two clothes dryers (there happened to be a spare), and six 1500W space heaters. 100A service.
| Thread Tools |