-   -   Main Breaker Tripping Due to Heat (http://www.diychatroom.com/f18/main-breaker-tripping-due-heat-153593/)
sinaial 08-13-2012 06:33 PM
I live in Arizona and I was told by my landlord's electrician that the main breaker tripped due to the excessive heat. Is this true? I owned my last house for 17 years and the electrical box faced the south and I never had this occur. Please help.
mpoulton 08-13-2012 06:38 PM
Elevated ambient temperature will cause a breaker to trip at lower current than it would otherwise, but rarely enough that a breaker will trip under normal usage conditions. Most likely there is another problem contributing to the situation. There may be a loose connection on the breaker causing abnormal heating, or the panel may be overloaded.
stickboy1375 08-13-2012 06:46 PM
12 Attachment(s)
I have to agree, your main breaker needs to be re evaluated, im just assuming, but i'm betting that it is damaged goods...
brric 08-13-2012 08:42 PM
What is the size of the main and HOW much load is on it.
gregzoll 08-13-2012 08:47 PM
I have only seen one load center breaker in my life that tripped in a hot space, and that was at 135 degrees that day in a boiler room. Turned out to be a faulty breaker. Replaced, never had the problem again.