What is the lubricant that is used on the main lugs of a service panel?
The reason I ask is a need to replace a MAIN panel on a remote barn on my property. I have access to a used, but in good condition panel that lacks the lube found in new panels. |
InPhase277 |
Actually its not ever required for aluminum, but knock your socks off... |
InPhase277 |
If it was so important dont you think it would be in the NEC? or required by a manufacture? and how do you know the damage was not caused from a loose connection, I have never seen any proof or research that Noalox does anything... I would spend my money on a torque wrench before I wasted it on Noalox... |
IMHO, I would think that damage from oxidation and damage caused by arcing are quite different from one another and easily distinguishable. |
I've even used noalox on outside connections in flood lights and on the threads of buried rigid and IMC. Better safe than on fire:furious:! How many other things does the code not require that you think should be in there? Anyhow, try passing an inspection in my area without it... InPhase277 |
Besides, I can't show you a picture of any oxidized wire because all mine are lubricated.:laughing: |
Here are some service conductors that had been "temp spliced" for about 20 years. All things considered, I was amazed at their good condition.
http://i8.photobucket.com/albums/a8/...2/DSC01453.jpg . http://i8.photobucket.com/albums/a8/...2/DSC01455.jpg |
Thanks buddie... :thumbup:
1 Attachment(s)
I don't believe antioxidant compound was ever required for the aluminum wire but for the termination lug and only if the manufactuer required it. Seems to me it was always stated that it was recommended. Also with the 'new' al alloys we use today it really isn't necessary... but to add noalox was the least liked by me whenever I used it... penetrox is a much better product IMO.
UL 486B (par. 7.5, p.12) "If specific instructions for assembling the connector to the conductor are furnished with the connector by manufacturer such instructions are to be followed in the preparation of the terimation except the conductor is not to be brushed or abraded and antioxidant is used only if the connector is pre-filled with the antioxidant. "From the white book" |
I HAVE however seen MANY oxidized aluminum wires.
The last couple were feeders...... underground PVC to a 100 amp apartment panel....maybe 4 years old. A slight nick in the insulation on installation combined with sitting in a water filled portion of the conduit turns the Al wire to white powder. I have not seen oxidized conductors in a dry location. |