If a 10 strand neutral wire has 2 of the wires burnt will this have any effect on the volts that it will carry? These are overhead. It looks like one hot wire may be burnt also. Curious
rich6111 is offline   Reply With Quote
Old 05-06-2013, 03:33 PM   #2
Special User
Rewards Points: 1,230
Under lightly loaded conditions, the voltage will be normal on a damaged conductor. As the amount of current drawn increases, the voltage goes down in proportion to the resistance and heat builds up at the damaged location, possibly leading to flames.
If it's damaged, why not replace it? Continuing to use damaged conductors won't save you any money when your house becomes a pile of ashes.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
The Following User Says Thank You to tylernt For This Useful Post:
MTN REMODEL LLC (05-06-2013)
Old 05-06-2013, 04:22 PM   #3
Rewards Points: 1,514
The voltage rating would be unchanged. For common wires in household usage the voltage rating is usually 250 volts or 600 volts and marked on the outside.
Two of ten strands is 20%. You could safely assume that you can run 80% of the normal amperes for example 16 amps (not continuous usage) for 12 gauge wire.
If you snipped off the end that only had 8 strands remaining, is it still long enough to reach the terminal or wherever it is to be connected?
AllanJ is online now   Reply With Quote
Old 05-06-2013, 05:36 PM   #4
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 2,846
You can PROBABLY get by with it under light,even moderate loads.... but is that SMART.
I agree with Tyler above (Warning ! I'm not a SPARKY, but a GC)
Isn't your real concern as to why they are burnt initially?
Best
Peter
MTN REMODEL LLC is online now   Reply With Quote
Old 05-06-2013, 06:03 PM   #5
dmxtothemax's Avatar
Rewards Points: 5,360
Indirectly YES!
Reduced wire size will decrease its amp carrying capacity !
So under heavy loads the mains voltage could decrease,
Under light loads it might be ok.
There are a few variables to consider.
But generally YES!
The wire might be savable,
but that decision should only be made by
an experienced electricain.
dmxtothemax is offline   Reply With Quote
The Following User Says Thank You to dmxtothemax For This Useful Post:
Old 05-06-2013, 06:11 PM   #6
Think of it this way maybe..... you have wire (at least a short piece of it which is just as dangerous) that is too small for it's breaker!
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Carrier weather maker 9200 furnace NO 24 volts mmtuxedo HVAC 1 09-25-2009 06:49 PM
Wire sizing to the condensor zootjeff HVAC 9 06-22-2009 08:02 AM
changing 250 volts into 115 volts hottlilmama Electrical 9 05-25-2009 09:33 AM
Does Home AC ever read 0 volts? step.gary Electrical 3 07-01-2006 03:57 PM