I want to double check my calculations for low voltage lighting. I Have a 15 amp circuit, with some outdoor 110v floods on it. With everything on, it draws 7.4 amps. I would like to T off the junction box with a line to a transformer to run some 12v deck lighting. I want to make sure I am under my max amps of 15.
The deck lighting I want to run, as I said is 12v. The fixtures are as follows:
15 x 11 watt fixtures
12 x 7 watt fixtures.
How many amps will I draw in addition to the 7.4A already on this 15A circuit? I calculated about 2.5 amps in addition to my 7.4, which puts me at about 10A on a 15A circuit.
LikeNew is offline   Reply With Quote
Old 01-02-2011, 02:01 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
You are adding a total of 249 watts of lighting or 20.75 amps at 12 volts. Assuming the lighting transformer is only 80% efficient (very worst case), that's about 2.6 amps at 120 VAC.
7.4 (existing load) + 2.6 (added) = 10 amps total
Coastal South Carolina
Old 03-31-2011, 04:46 PM   #3
Another way to calculate
I take the 12V wattage and divide by 120 to get the amps the low voltage lighting is using. 249 watts / 120 is a little over 2 amps.
Utah Lighting is offline   Reply With Quote
voltage on earth wire Spikeyboy Electrical 13 10-15-2010 12:03 PM
Voltage in Metal Roof and Gutters TITAN2390 Electrical 4 10-07-2010 08:44 PM
New recessed lighting: Line Voltage vs. low voltage hyunelan2 Electrical 0 10-12-2009 01:25 PM
Low voltage box question WShawn Electrical 7 08-19-2008 07:22 AM
2x100a sub on service main jambud Electrical 17 03-12-2008 10:31 AM