I am going to run electric to a pier from the main panel. I will be connecting to a 60 AMP sub panel at the pier. I believe I need to use THWN in a PVC conduit, bu am unsure about GA. The run is 350 ft. in an 18" trench. I have been told AWG 4 with a 6 ground upto AWG 8 with a 10 ground. I know power drops with distance, but I can't seem to get consistent answers. All advise is appreciated.
It really depends on what you plan to power at the pier. Do you have any idea what the power requirements will be? Are you doing just lights and convenience receptacles or are you planning to run a motor such as an irrigation pump or boat hoist?
As a practical matter, at that distance, I wouldn't run anything smaller than #6 (you will need three) with a #10 ground.
This project is more complicated than just finding the right wire size. I would first contact the AHJ as to his requirements regarding piers and floating docks.
NEC rules concerning docks and piers must be followed. This is a potentially dangerous project for someone who is not qualified.
Please get a qualified electrician for this job. And have the blessing of the local AHJ before doing any work.
This application could have lethal affect not just for your pier, but anyone who uses the waterway. :no:
J.V., Thanks for your concern, but you sound like a permit clerk. The work is being done by a licensed electrician and my neighbor is a county bulding inspector, so it will be code.
I was asking for educational purposes and thought this might be a good forum for enlightenment.
The voltage drop will be relevant to the voltage at the wire runs source. By this I mean if the voltage at the panel where the feeder originates is 215 volts then that is about the lowest for a motor to operate at peak efficiency. This would mean I would have to put down wire that would'nt allow any voltage drop for 350 feet. This is of course considering you want the hoist motor to receive it's rated voltage.
When I calculate this for 40 amps demand (60 amp sub-panel) I get #3 awg copper conductors and a #4 awg copper ground wire considering 240 volts at the source.
8 awg copper needed for 40 amp circuit...no voltage drop
#10 ground needed
#3 awg copper for 40 amps at 350 feet from the main panel not over 3% VD at 240 volts.
? ground wire needed
#8 awg copper is 16510 cir-mil
#10 awg copper is 10380 cir-mil
#3 awg copper is 52620 cir-mil
52620/16510 = 3.187......so # 3 awg is a little over 3 times larger in cir-mil than #8 awg
This would mean we would have to increase the ground by a factor of 3.187
3.187 x 10380 = 33,081 cir-mil
Chapter 9 table 8 shows a #4 awg will be required for the equipment ground.
I can list a general guide line for the electrical installation for a private dock if you like . Just ask and I'll put it up.
Note the NEC doesn't address private docks this is an area that is local code sensitive.
This wire is gonna cost you a few thousand dollars lol. Did you size this in copper because of the damp location and the corrosion factor in aluminum? Just curious.
For 350 feet run of wire you are talking about the size #3 which it will meet correct VD @240 volt [ 6.9v drop ,2.9% ] typically i keep at least under 3% drop the max.
but for privte docks there are some code it will cropped up and the materals you will have to use.
mantory GFCI is a must. [ note that in 08 code cycle the 240 v boat lift will required a GFCI so just a head up with it .]
it will have 4 wire circuit set up 2 hot 1 netual 1 ground the size will be #3 for hot and netrual but for ground can squeak by with #8 but rather upsized to #6 due the distance
[ the reason why i say upsized because i allready dealt with alot of parking lot luminaires they have pretty good distance to cover so that why i recomoned to upsize grounded wire a bit.]
Richyl .,, any underground conducts are automatic wet location it is not a damp location at all.
well with alum wires if done propely it should not be too bad but for docking area it will be much better stay with copper wire anyway.
I can pretty well assure you that copper wire will be required. There will also need to be a grounding electrode at the sub-panel. The sub-panel likely will not be allowed on the dock.
Typical private dock wiring description (for example only) you must check with your local code requirements for specifics.
The caption at the top is important: "local codes may vary". Around here, the Corps of Engineers requires the entire run to the dock subpanel to be GFCI protected because it will cross public (Corps) property.
Yes... this is very true about codes differing. I had planned to put all those possibilities in the drawing with side notes but I wasn't able to figure out how to keep the file size small enough to attach the drawing. Limited to 97.7 kb on this site. I'm still working on some of the ways to get more info on the drawing but as you can see it is getting rather busy. But is a good reference for general thoughts for someone with a project that has to do with floating private docks. All shore power outlets have to be gfci and that needs to be in the drawing so as you can see it is a work in the making.....
BTW.... Thanks for the input I changed the drawing to reflect a gfci feeder
Thanks for all the useful info. Yes, it will definately be copper, and the sub-panel will be mounted on a post about 10 feet from the shore.
As far as, ' If I have my own pier, i am not worried about the money'.
If when I bought the house, 8 years ago, it had had a pier and boat lift, and I didn't have to remove 4 commercial dumpster of yard waste, and I hadn,t had to completely remodel, rebuild the house, then yes I would not be worried about money.
However, it was a fixer upper and I am just now getting to the pier.
Thanks again for the input, and BTW, the view is fantastic.