Old 03-08-2013, 09:11 AM   #16
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Size of wire
Hard to say from what you listed but typically a 6/12 100 amp sub-panel is used for docks either on a pedestal shore side (type 3R) or on the dock in a rainproof closet. Now the 100 amps is way more than you need but if allows enough circuit breaker spaces to provide for boat lifts, receptacles , and lighting. Your can power it with less than 100 amps say 50 or 40 amps. All wire must be insulated and color coded and rated wet location. No aluminum wire.
Determine your load at the dock under the heaviest possible load screnario. Use an online voltage drop calculator like here ... Use 240 volts as your supply voltage to control your wire size.. 120 volts for the feeder IMO will create too much voltage drop depending your loads especially lift motors. If you plug both into the voltage calculator you will be able to compare the differences. 240 volts will also give you some nice options for dock specific lifts with 240 volt motors and other equipment. Remember everthing must be gfci protected.
http://www.electrician2.com/calculat...alculator.html
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 03-08-2013, 10:36 AM   #17
Rewards Points: 204
Remember that the wire is heavy and will want to drop down this embankment. You might require wedges designed just for this purpose. I would hate to see you pull all that wire in, just to find it in a pile at the bottom the next day. Ask your electrician.
The Following 2 Users Say Thank You to J. V. For This Useful Post:
jbfan (03-08-2013), Stubbie (03-08-2013)
Old 03-08-2013, 02:56 PM   #18
Rewards Points: 348
Originally Posted by al_smelter View Post
I spent last summer camped next to a family whose son was killed two years ago when electrocuted jumping off of a dock in West Virginia. It's a sad story.
It is sad, but if it is the story I am thinking about, it is not related to a dock. A houseboat was leaking current into a lake and when the boy grabbed the ladder to climb back up on the boat, he was electrocuted.
herdfan is offline   Reply With Quote
Old 03-08-2013, 11:09 PM   #19
dmxtothemax's Avatar
Rewards Points: 5,496
Are the two lift motors used at the same time ?
If so thats 30a already,
leaves very little for the other outlet and lights !
Consider using bigger cable I would go for
something like 60a cable.
Is there going to be 240 or just 120 ?
dmxtothemax is offline   Reply With Quote
Tags
conduit , gfci , wire sizing
Attic project - Would like opinions whataboutj Insulation 6 06-29-2011 03:07 PM
Anyone used a project manager instead of GC? pulpit Building & Construction 10 02-11-2011 10:08 AM
My project... The Cable Guy Electrical 10 01-02-2011 09:14 PM
Interesting Project Mcamnl Electrical 14 05-27-2009 01:13 PM
Basement Renovation Project Howdy Electrical 6 03-13-2008 11:07 AM