What do you see that's wrong with this load center?
It's mounted on wood, shouldn't it be on drywall?
Thanks to EBFD6 for the picture.
Lurlene is offline   Reply With Quote
Old 09-28-2010, 03:11 AM   #2
" Euro " electrician
frenchelectrican's Avatar
Jezz there is plenty things are wrong I almost dropped my breakfast to floor when I look at the photo.
Now is this main service cable is from bottom feed ? if so why not inverted the box in irst place so it don't have to bend the bloody big cable like that.
Second I don't see the EGC there unless it is buried somewhere.
Is this load centre a real main breaker useage or use as subpanel ?
If latter that is a major code voliation.
Now for the rest I don't see any NM staples on the NM cables it have to be withen 12 inches from the box { that is easly corrected }
I did see one good issue look at the two pole breaker you have two breakers with two conductor and the other one with single conductor that is a no-no at all { I know SqD QO series are listed for two conductors under 30 amp size }
two -two pole breakers with unremarked white conductor that should be marked for 240 volts load.
Double up netural conductor at the netural bussbar is a major no-no
I know you will ask about plywood over the drywall well.,
Some wall have nonstandard stud spacing and if the box will not able hit one of the two studs then we will put in a plywood to support the load centre unless you got a good 14.5 inch spacing between the studs then it will be sunk in the wall without issue.
The other reason why I rather put a plywood on the wall if nonstandard spacing or must have to surface mounted for good reason then I will use the plywood instead of drywall due the weight of load centre it can get pretty hevey and the drywall will not support the weight of load centre plus the numbers of conductors that can add up weight pretty fast.
I don't know if my eyes are teaseing me but look like at least two NM cable did not have any NM clamps there. { on left side of load centre}
Oh yeah I will never use the drywall screws to support this big of load centre like that.
If you want my grade on this one.,, it is D-
Merci.
Marc
Old 09-28-2010, 06:44 AM   #3
Master Electrician
Rewards Points: 3,698
If it's a main panel I can't see a bonding screw.
brric is online now   Reply With Quote
Old 09-28-2010, 07:01 AM   #4
Very sloppy, which will attract closer attention from the inspector, once he stops laughing.
Old 09-28-2010, 10:46 AM   #5
Licensed Pro
Better question would be:
"What do you see that's RIGHT with this load center?"
Old 09-28-2010, 04:26 PM   #6
Thanks for the insight!
I haven't seen many load centers, that's why I'm asking.
Here's what I see that doesn't make me drop my breakfast:
No burnt or melted parts.
No double wires to one breaker screw.
One open space for another circuit.
Thicker wires going to the 240V breakers, mostly.
Can you tell me what would be laughable about this object?
Old 09-28-2010, 06:08 PM   #7
Electrician
Rewards Points: 760
Even if there were #14 going to a 240V breaker, what would be wrong with this as long as the wire was sized properly to the breaker capacity.
darren is offline   Reply With Quote
Old 09-28-2010, 07:20 PM   #8
The fact that in the original picture- before being cropped -it showed the wires coming up from the floor
And the breaker panel was installed in a room on the wall
Here is the 2nd picture:
Old 09-28-2010, 07:32 PM   #9
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 46
LOL WHY would they install the panel in a room upstairs? It's obvious the feed is in the basement, and all the wires are going there, so why not just install it there? That is hilarious. i can now picture the home owner wanting to hide that and doing ridiculous code violations like shoving a huge heavy dresser in front of it, or something.
And do I see ground wires connecting with neutrals? Even if it's the main, that's a big no no right? I figured they still had to be on seperate bars, just that the bars are bonded.
Old 09-28-2010, 08:15 PM   #10
Electrical Contractor
kbsparky's Avatar
Some houses do not have a basement. Around here, most of `em have a crawl space with about 3 feet or less clearance.
Where is the meter box on this house? Just outside the window, behind the panel? Or elsewhere?
I agree that it would have been a better installation with the mains at the bottom.
As for the neutrals and grounds, IF the panel is the service entrance, then you can mix `em on the same bus bars. As long as you only have one neutral per terminal, you're good to go!
-KB
Load center to use bob22 Electrical 2 11-07-2009 05:28 PM
Meter Load Center Combo mikkyle Electrical 4 10-30-2009 06:49 PM
Gen-ready load center for CH breakers i6pwr Electrical 2 08-23-2009 12:09 PM
Sub Panel Main Lug Load Center - Single Phase ? Roy Rowlett Electrical 21 08-20-2009 07:55 PM
Moved ceiling light in bedroom to center, now trips breaker blthomas Electrical 18 01-24-2008 05:29 PM