Load Center Replacement - Electrical - DIY Chatroom Home Improvement Forum
Old 04-08-2013, 08:31 PM   #1
Hi, I'm in the process of replacing the original load center (35-40 yrs old) in the garage and I'm looking to get some advise on a suitable replacement. Here's the current set up:
At the outside service entrance I have a 100amp breaker adjacent to the residential service meter. This service breaker connects to a 125amp/24 pole main breaker panel in the garage.
The question: Is it better to stick with the 125amp / 24pole or would a 100amp / 32pole load center be equally suitable? I'm thinking that with a 100amp breaker at the service entrance I'm limited to 100amps anyway - correct? (And the extra space in panel would be nice....)
dfelb8 is offline   Reply With Quote
Old 04-08-2013, 08:51 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 224
With the 100 amp breaker outside, you could put in a 200 amp panel if you wanted to.
The panel would be protected by the 100 amp breaker.
Is space the only concern, or just the age of the panel?
Old 04-08-2013, 09:20 PM   #3
The original load center is a FPE stab-lok which I now understand to be a fire hazard. That is reason number one for replacement. Reason 2 is breaker selection and reason 3 is expansion. It seems the common practice is to add a subpanel if you run out of breaker space and the tandem style cannot provide the remedy. I'm thinking if I had 32 circuits instead of 24 I could avoid the subpanel scenario.
Also, you bring up a good point of clarification. Its seems that exceeding the amp rating is common practice. Example - Home Depot sells a 100amp/32 pole load center with 5 20amp single breakers included. If 100amp was the true ceiling of the panel then what would I use the other 27 circuits for? (Presumably this means not more than 100amps total are in use at any one time).
I wouldn't mind putting in a 200amp replacement but that is dependent on the conductor size coming from the service entrance - correct? What gauge would I need to allow for the 200amp load center?
Old 04-09-2013, 12:57 AM   #4
Rewards Points: 512
At the outside service entrance I have a 100amp breaker adjacent to the residential service meter. This service breaker connects to a 125amp/24-space main breaker panel in the garage.
The breaker near the meter: is it in a 100amp disconnect box (has only one breaker in it), or are there spaces for other breaker too? Doesn't really matter, I was just curious, for my own edification
Anyhow, a 200 amp panel in the garage (I assume it's an attached garage?) would require 4/0 AL, or 2/0 CU.
Its seems that exceeding the amp rating is common practice. Example - Home Depot sells a 100amp/32 space load center with 5 20amp single breakers included. If 100amp was the true ceiling of the panel then what would I use the other 27 circuits for? (Presumably this means not more than 100amps total are in use at any one time).
Forget that! The sum of the individual breakers do not indicate the ampacity of the panel. Not every circuit will be in use at the same time, you won't be running both the AC and the Heat, and not every circuit will be loaded at its capacity.
sirsparksalot is online now   Reply With Quote
Old 04-09-2013, 03:20 AM   #5
Electrician
Rewards Points: 150
No. You can feed a 200A panel with 30A breaker and wire. If the load calculation says ok it's perfectly legal, but silly.
In your case there just wont be 200A available until you upgrade the service and feed. Until then the 100A breaker near the meter will limit what the panel can draw.
A residential load calculation will tell you if the house has outgrown the 100A service.
Every load center has a label inside the front cover. A range of wire sizes will be listed for the lugs and/or the main breaker. Do not put a wire in a terminal if it does not fall in its listed range. To fix an out of range wire you can either splice a short piece of wire that is a correct size or backfeed a smaller breaker. Smaller breakers also have wire ranges written on them. And backfed breakers need a special retainer.
It is a good idea to have enough full spaces for every circuit, and extra for future expansion. It is a bad design to have a new panel with any tandems or quads.
Glennsparky is offline   Reply With Quote
Old 04-09-2013, 01:44 PM   #6
Great feedback all - thanks! I confirmed that the wire coming in at the service entrance and the wire from the service panel to main breaker panel are both 2 gauge aluminum. Based on this I think I will go ahead with a 200amp main breaker panel/load center in preparation for a Service change to 200amp shortly down the road. In the meantime the main breaker panel in the garage will not get more than 100amps and I'll use that as the guide/threshold for power consumption.
Please advise if any major concerns with this plan of action....
Main load center grounding question. sgip2000 Electrical 18 10-03-2012 12:45 PM
Boxing In My Load Center? ddawg16 Building & Construction 5 08-22-2012 11:21 PM
portable generator to load center old blue Electrical 1 07-06-2012 01:41 PM
Installing new load center - do I have to buy AFCI breakers jerseyguy1996 Electrical 6 11-01-2010 10:29 PM
Load Center Replacement Question EmilG Electrical 10 09-29-2010 01:11 PM