Old 06-17-2011, 09:03 PM   #1
Live wire cut
I cut through a live wire. Now the wire is dead but no circuit breakers tripped.
larrbuzzaw1 is offline   Reply With Quote
Old 06-17-2011, 09:14 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 488
What was the wire feeding?
Look for a tripped gfci.
Most breakers trip to the center position, and must be turned of to be reset.
Old 06-17-2011, 09:23 PM   #3
joed's Avatar
Rewards Points: 12,918
Fix it. You give us much to go on, so I give some basic advice.
Splices MUST be in accessible junction boxes. So you will likely need two boxes wit ha cable in between the make the wires long enough to go into the boxes.
Or replace the cable with a new one.
Old 06-19-2011, 07:41 PM   #4
After some investigation and suggestions from this thread and friends, I tried to trace the wire to its breaker and no luck. Then someone suggested if there was another box somewhere. I have a manufactured home in a 55+ community. There is a panel below the meter that is outside that had 3 additional breakers. I was not aware of this type of setup. So I ran splice between the burnt wire with 2 junction boxes, ran the wire through the rafters and down inside the wall to the other junction box. Now everything is legal and I can close everything back up. Thanks all for your help. Larry
Old 06-19-2011, 07:49 PM   #5
jbfan's Avatar
Rewards Points: 488
Glad you found the problem, and repaired it correctly!
Good Job.
Changing Two Gang Outlet to Three Gang Outlet vbullinger Electrical 9 01-10-2011 05:13 PM
HVAC three wire motor to six wire motor Leo Caproni HVAC 5 10-18-2010 01:23 PM
Safe way to determine if a wire is live? Fortitude Electrical 15 10-03-2010 08:00 PM
Outlet With Swith and Older (White, Black, Red) Wire CaptChaos Electrical 18 09-14-2009 11:17 PM
Stranded wire on screw connections BigJimmy Electrical 7 01-19-2008 02:42 PM