#16 |
Lights not working
No, the bedroom and bath are the closes to the garage where the breaker box is.
All the outlets work fine. It is just the light. You are probably correct that it is the same breaker that supplies the power. It would be very weird if they were separate and went out at the same time. Did you mean a break in the wire? This is interesting because the house is only 1.5 years old and I would not expect anything like that to happen so soon. It has been very cold recently. If this is the case I am assuming I will need to have the wire replaced. Thanks a lot for all you help. |
#17 | |
Lights not workingQuote:
#18 |
Lights not working
I am sorry, I am not familiar with the terminology. When you say bad connection in a wire nut or a back stabbed receptacle, what exactly are we talking about.
Also, should I call an electrician for this? I am not sure how to find a fault in a wire without cutting it and retesting. I am sure there are better ways. Thanks again |
#19 | |
I think there is a bad connection in one of the wire nuts or at a receptacle so no power goes to the switch. |
#20 |
Lights not working
Once you described them I know exactly what you are referring to. I will check them out. If I don't get anything I will call an electrician. Thank you again for your responses.
#21 |
Lights not working
No problem. Be safe. 120V can kill you with no problems whatsoever.
#22 |
Lights not working
I'm going to make the random guess that the breakers have been misidentified.
One breaker is labeled for the bedroom, one for the bathroom. I'm randomly suggesting those are for the bedroom outlets and the bathroom outlet(s), respectively. I'm going to guess that the lights are on a different breaker, which may or may not be tripped. Two circuits don't both develop random opens at the same time. An open neutral on a shared-neutral circuit will leave both of the downstream loads in series with each other across 240. One side will get OVERvoltage. Both offending lights are on the same circuit and there is one problem - either a tripped breaker or ONE bad connection. |
#23 |
" Euro " electrician
Lights not working
Ok Now I can see where this goes and this OP did have AFCI breaker per NEC code requirment but the bathroom have standard breaker due he have the GFCI receptale there in the bathroom.
Now most likey a connection issue either at the switch or at one of the wirenuts on that affected circuit. Check the bedroom receptales to make sure you are receving power if so then you will have to check the switch box to make sure it is good and tight. If some reason if you are not confortable you can call in electrician. or someone who know the electrical system very well. Merci, Marc |
#24 |
Lights not working
I'm not differing from frenchelectrician's statements at all - where he's going is what you need to do if, in fact, there's a problem.
Just reiterating however: I think, based on the information provided thus far, that it is HIGHLY likely that the offending lights are on a circuit OTHER than the two that have been tested, and it can't hurt to test (and/or cycle) ALL of the breakers in the panel before digging into the wiring. |
| Tags |
loss of power, no lights ![]() |
| Display Modes | |
| Finding underground electric wire for driveway lights. | mitch21131 | Electrical | 25 | 09-24-2012 09:52 AM |
| Help with Two Switches & Two Lights | simplyphp | Electrical | 36 | 11-25-2010 03:47 PM |
| How do I connect one switch to 3 lights? | Dorkus | Electrical | 9 | 09-27-2009 11:08 PM |
| New lights in basement | CooperChloe | Electrical | 11 | 01-11-2009 12:22 PM |
| adding lights | mharwell01 | Electrical | 1 | 01-03-2009 04:59 PM |