Lights Get Brighter When Load Starts? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-26-2013, 08:45 PM   #1
Rewards Points: 156
Lights get brighter when load starts?
I was at a friend's house helping him install some track lighting in his basement. We installed LED bulbs in the track lights and connected them up to a dimmer. We were sitting down admiring our handywork when his oil boiler lit up. WHen it started, we were expecting the lights to dim a little, but the LED lights actually got brighter during the momentary surge the boiler made. WHat's up with that?
av-geek is offline   Reply With Quote
Old 03-26-2013, 08:58 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 656
A loose neutral connection some where.
Any other lights do it?
Do some get dimmer as well?
Old 03-26-2013, 09:04 PM   #3
JOATMON
ddawg16's Avatar
Rewards Points: 2,142
Yep....or the transformer is going....happened to us...
Take a voltmeter and measure the voltage at the load center
You need to do the test twice....
Measure from one side to neutral....turn on a heavy load such as an iron....
Repeat the test on the other leg.
If the voltage goes up on one leg but drops on the other....you have a bad connection before you load center or the transformer feeding your house has an issue.
If no significant change (2 volts or less), then you have a loose neutral somewhere in the load center our down stream.
In my case, just turning on table saw cause a 13v rise on one side and 13v drop on the other....the power company replaced the transformer post haste....
ddawg16 is online now   Reply With Quote
Old 03-26-2013, 09:10 PM   #4
Idiot Emeritus
Rewards Points: 1,492
Classic symptom of a loose neutral.
It could be anywhere from the utility transformer all the way to a 12/3 or 14/3 that feeds the circuit in question.
When a load is applied, look to see if lots of lights brighten or just a few. Some will dim as well. If just about everything brightens or dims, the problem is in the panel, meter base or the incoming utility lines.
If just a few things brighten or dim, it's more likely in a 3 wire cable that feeds the offending loads.
Rob
micromind is offline   Reply With Quote
Old 03-26-2013, 10:17 PM   #5
joed's Avatar
Rewards Points: 13,766
Agree classic indication of a loose neutral. Also very good chance of damaging any electronics you have. Unplug anything important you don't want damaged.
Arcing between circuit breakers and flickering lights mscotter Electrical 12 07-13-2012 12:46 AM
Lights still dimming and flickerin Keisha34 Electrical 18 06-08-2012 11:14 PM
Dimming and Flickering lights in home Keisha34 Electrical 34 06-05-2012 02:22 PM
Help with Two Switches & Two Lights simplyphp Electrical 36 11-25-2010 02:47 PM
New lights in basement CooperChloe Electrical 11 01-11-2009 11:22 AM