Light Turns Itself Off - Electrical - DIY Chatroom Home Improvement Forum
Old 06-16-2014, 09:57 AM   #1
psp
Rewards Points: 90
Light turns itself off
So we had a new furnace and AC unit installed. However, our kitchen light now works for only about 10 minutes and then turns it self off for about 30 minutes. The problem started right after the furnace and ac install. Is this a coincidence? Separate breakers etc... I am confused.
I replaced the switch - nothing changed.
I don't have any instruments to test the power to the light etc...
Could it be the light itself. It is a chandelier style with multiple bulbs. Has worked perfectly for about 5 years until the new AC / furnace install - very odd. Can lights regulate themselves and turn themselves off for a time period? Why?
Maybe I need a need a new kitchen light? The light was expensive however. Odd that it all started right after the install of the furnace and ac
Ideas on how to fix this?
Thank you
psp is offline   Reply With Quote
Old 06-16-2014, 10:23 AM   #2
Rob
Robpo's Avatar
Rewards Points: 826
Thank you
You need either a electrician, a tester, or try replacing the light or bulb.
I don't know what other advice to give.
Robpo is offline   Reply With Quote
Old 06-16-2014, 03:05 PM   #3
Thank you
I'd bet a loose connection in the circuit to the light fixture.... current flow heats up the connection and it comes loose enough to break the circuit. Once the connection cools down, it works again. The recent AC work may be a red herring (perhaps the installers were in the attic and jarred the junction box enough to make a poor connection even worse).
I'd start by killing the breaker to that fixture, taking it down and examining the connections in the ceiling box. If it is a poor connection, you'll probably be able to tell based on charred wire nuts/wire insulation. If it, clip a little off the wire ends, restrip them and then remake the connections with new wirenuts. Make sure the box is grounded (if there is a loose connection, a properly grounded box could be the difference between a tripped breaker and a fire).
clashley is offline   Reply With Quote
Old 06-16-2014, 03:26 PM   #4
Rewards Points: 3,396
Sounds good.
I would check panel connections, and other easier to get to points before dropping the fixture.
You said both chandelier and high hats, so check boxes that would be common to both.
Yes you will need a tester, and you might want to trouble shoot when it's out.
ritelec is offline   Reply With Quote
Old 06-16-2014, 05:20 PM   #5
dmxtothemax's Avatar
Rewards Points: 5,610
For sure it's a loose joint/splice somewhere.
Before with a reletively light load it was working,
But now with the extra load on the circuit it becomes an issue !
Could even be a loose/faulty breaker.
But the concept remains the same.
dmxtothemax is online now   Reply With Quote
Old 06-17-2014, 08:38 AM   #6
Bill Kearney
Rewards Points: 1,174
Unless the wiring for the light is near the wiring for the furnace, it's very likely the breaker. Breakers do fail. It's possible yours was on it's way out. And when they were figuring out which breaker controlled the furnace they turned off the one for the lighting. This could have revealed the sorry state of that breaker. There's next to nothing they could have done to it to damage it. Fortunately most of them are relatively cheap and easy to replace.
wkearney99 is offline   Reply With Quote
Old 06-17-2014, 10:19 AM   #7
Not to say that breakers don't fail. BUT, I've NEVER had a troubleshooting call and the fix was replacing a bad breaker.(single pole 15's,20's)
Maybe a loose connection at the breaker , neutral, or in the field. faulty switches, back stabbing, etc.. etc..
Again, not that it doesn't happen.
(would a breaker heat up, turn off, then cool down and turn back on?)
I must mention that I will check though to make sure all the breakers do have power on them (you never know).
Check the panel.
edit: As mentioned, could be coincidence the ac install and that circuit. Just came back from a service call where lighting in laundry/bath was out.
Cause, back stabbed receptacle two rooms away.
good luck
The Following User Says Thank You to ritelec For This Useful Post:
wkearney99 (06-17-2014)
Pilot light button on furnace won't turn whydonchathen HVAC 8 01-19-2015 10:40 AM
Bad home wiring? Turn off light-internet drops or motion light turns on drewryjams Electrical 2 07-30-2012 03:55 PM
Rerouting Bathroom Wiring roasted Electrical 36 05-13-2012 09:58 PM
Ceiling Fan with Light kit - Light not working aadams Electrical 12 11-03-2010 06:32 PM
Marmoleum repairs muggyfrost Flooring 8 10-16-2008 08:19 PM