I checked the voltage of incoming hot to the switch box and wire going to the light. With small load, voltage holds steady at 123.4V or 123.5V. With load, voltage fluctuates between 123.1 and 123.5, the small fluctuating seems to match the rate of light flashing.
xiea is offline   Reply With Quote
Old 04-27-2012, 12:49 PM   #17
If this is florescent I would try another bulb. That is a tiny variation, my voltage fluctuate that much and more all the time and nothing flashes.
bill01 is offline   Reply With Quote
Old 04-27-2012, 01:15 PM   #18
I=E/R
a7ecorsair's Avatar
You will need something other than a meter to see these voltage fluctuation because a meter doesn't respond fast enough; an oscilloscope would.
The device isn't the problem. The switch doesn't know about the receptacle and the receptacle doesn't know about the switch.
The problem is resistance on either the hot or neutral before this switch/receptacle device.
light switch/outlet combo, load issue-combo-device.jpg
a7ecorsair is offline   Reply With Quote
Old 04-27-2012, 04:35 PM   #19
When you say device isn't the problem, are you referring to the switch/outlet combo not a problem? So I don't need to bother replacing it?
The only wiring I did is the neutral by attaching a pigtail wire to the existing wire nut that holds the other white wires together.
Old 04-27-2012, 04:50 PM   #20
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
Make sure that you have a good connection on that pigtail.
Pull the wire and see if you can pull it from under the wirenut.
Old 04-27-2012, 07:19 PM   #21
I checked neutral and it's wired tight.
Old 04-27-2012, 07:33 PM   #22
jbfan's Avatar
Rewards Points: 552
I think it may be time for some pics.
Old 04-30-2012, 07:25 PM   #23
I replaced the switch/outlet combo to eliminate another possibility. Problem is still there. I plugged a hair dryer into the outlet and the light dims (not flickering), The higher the hair dryer setting, the dimmer the light becomes. Not sure what to do next.
Old 04-30-2012, 07:26 PM   #24
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Do the lights stay dim the entire time the hairdryer is on?
Old 04-30-2012, 07:52 PM   #25
Yes, the lights stay dim at the same level. Low setting on the hairdryer causes a slight dim to the lights and it will stay that way unless I either turn the hair dryer off and lights return to normal or if I turn the hair dryer to a higher setting then the lights dim some more.
Old 04-30-2012, 07:56 PM   #26
k_buz's Avatar
Do you have a second hairdryer to try?
Old 04-30-2012, 08:06 PM   #27
I only used a hair dryer as a secondary test. The original problem I encountered is plugging in a 660W appliance and when it's on standby there are no issues, when appliance starts, the lights flicker until appliance goes into standby mode again. I don't think hair dryer is the issue.
Old 04-30-2012, 08:12 PM   #28
I=E/R
a7ecorsair's Avatar
This is correct
So you found out...
Your voltage drop is somewhere before this.
This appliance you mentioned, does it have any type of motor?
Old 04-30-2012, 08:15 PM   #29
This is correct
So you found out...
Appliance has a heating element and possibly motor, not sure. I also tested plugging in hair dryer. Result was lights dimmed proportionally to the power setting on the hair dryer.
Old 04-30-2012, 08:19 PM   #30
k_buz's Avatar
Plug these items into a separate lighting circuit. Into a living room outlet or a different bedroom outlet, not the kitchen counter top outlets, bathroom outlets, or dining room outlets.
Turn on all the lights in the house and see if this happens on other circuits as well.
Tags
load , switch plug combo , wiring
ceiling fan light issue after replacing electrical panel texan206 Electrical 3 04-21-2012 11:33 PM
Ceiling Fan And Light Combo alphyone Electrical 1 05-20-2011 03:34 PM
Whirlpool Microwave light issue mustangcobra44 Appliances 8 08-14-2008 03:52 PM
replacing vanity light...issue with outlet box? tarheelblue Electrical 5 01-28-2008 09:20 AM
Light fixture issue baustin Electrical 4 07-17-2007 04:01 AM