I put an addition on an out house of mine and I am running 14 awg UF to it so I can get some lights and what not. It is about a 150 foot run back to the panel. I know 14 awg is rated for 15 amps, but for how long of a run...I want to know if I can run power tools off this line?
TBFghost is offline   Reply With Quote
Old 08-21-2009, 01:29 PM   #2
BCSparkyGirl's Avatar
I don't know where you are writing form, I know the CEC had a table I can calculate this out for you exactly, but if you are in the US, the I dont' know what the NEC req are. I would probably run a #12 to be safe, only saying this cause I am on vacation and away from my code book.......
BCSparkyGirl is offline   Reply With Quote
Old 08-21-2009, 01:45 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
It's not worth running #14 for a run like this, let alone for 150'.
No, IMO #14 is not enough to run power tools, especially something like a 15A saw, for a distance like that.
Speedy Petey is online now   Reply With Quote
Old 08-21-2009, 02:48 PM   #4
I also am away from my code book, but i would suggest just going with a 12awg to be safe. Remember it's always better to be safe than sorry.
Paelectrican is offline   Reply With Quote
Old 08-21-2009, 02:52 PM   #5
Not really.
Skillsaw, no.
3/8 drill, yes
Compressor, no
Battery charger, yes
220/221 is offline   Reply With Quote
Old 08-21-2009, 03:19 PM   #6
15A, 5% drop @ 120v, #14 AWG copper, max length = 77'.
", ", #12 AWG copper, max length = 125'.
Old 08-21-2009, 03:34 PM   #7
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Originally Posted by 220/221 View Post
Not really.
I agree with 220/221 that the Yes/No answer depends on the load.
The total 14 AWG conductor length resistance with my table comes out to .773 Ohms.
This number by itself doesn't look scary, but at 120V a 15 Amp load will cause an IR drop of 11.6 Volts. Looking at a 10% IR line drop at 120V still doesn't look particularly scary, but TBF needs to look at the power equation.
The Power delivered is E
/R.
If TBF connects a 15 Amp load the Power is cut by 20%
Note: the voltage drop is over the total conductor length which in this case is 300'
Disclaimer
& Stay Safe
.....Bob Lavery
Old 08-21-2009, 07:17 PM   #8
Idiot Emeritus
Rewards Points: 1,492
For 150', I'd run at least a 12/2, better yet, a 10/2.
A 12/3 or 10/3 would be even better, that way the loads (lights/receptacles) could be split among two circuits.
Rob
micromind is offline   Reply With Quote
Old 08-22-2009, 12:09 PM   #9
Rewards Points: 168
Is this truly an "out house" or an out house? If its an out house where you crap in it. You may want to go big enough for heat and a light.
Old 08-22-2009, 12:38 PM   #10
For 75 C conductor temp. you may want to reduce my lengths by 20%.
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-25-2011 11:29 PM
pre-hung door, 32x80 is that door size or total size? RyanD Building & Construction 3 06-28-2009 10:33 PM
Room size X floor tile size deck hand Flooring 4 04-08-2009 04:42 PM
duct work size justmefixin HVAC 2 09-20-2008 06:59 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM